Smart 1500 LCD & Green Mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart 1500 LCD & Green Mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
7
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

Smart 1500 LCD & Green Mode

Is there a way to turn off the Green mode on this model? I'm looking to see if I can get the unit to output a steady 230v or 240v for a period rather than follow my normal input which can float around quite a bit.

I have a 9630 NMC card installed, but cannot an option in there or via the menus on the unit itself.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

in our 6.x NMC firmware due later in December, the NMC will give you the option to toggle Green Mode on/off. today you cannot do it via the NMC. you'd have to adjust the setting via the front panel of the UPS via the LCD.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

Thats interesting over the NMC firmware option, I couldn't find it via the control panel on the front either - can you give a pointer as to where to look?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

>
Is there a way to turn off the Green mode on this model? I'm looking to see if I can get the unit to output a steady 230v or 240v for a period rather than follow my normal input which can float around quite a bit.
>

Which model UPS is it? If it's an SMX or SMT unit, the line interactive topology won't give you tight voltage regulation unless running on battery. SmartUPS Online UPSes, on the other hand, can do this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

Interesting, I thought the units have a Boost and Trim Automatic Voltage Regulation system which can be turned on (by turning off green mode) which seems pretty good. I have a larger (SMX3000RMHV2UNC) Smart Line-Interactive UPS and it will keep a pretty steady output even when not on battery. The feature list for AVR does say it is not supported on all models, but I cannot find out which models the feature is on.

I did go through the Advanced menus too and couldn't find the option, so I suspect my model (SMT1500I) doesn't support the feature.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

>
Interesting, I thought the units have a Boost and Trim Automatic Voltage Regulation system which can be turned on (by turning off green mode) which seems pretty good.
>

The unit will leave green mode if it needs to boost or trim.

See the [SMX / SMT FAQ|http://nam-en.apc.com/app/answers/detail/a_id/10816/~/frequently-asked-questions-for-the-new-smx-and....]:

>
How does the ‘green’ operating mode increase efficiency?

APC’s patent pending ‘green’ mode bypass components that perform automatic voltage regulation (AVR) when not needed. AVR is typically handled in the line interactive design by solid state transformers. These transformers, while extremely reliable, do have some energy loss to remain energized. By using these transformers only when needed results in higher efficiencies across a wide range of load conditions.
>

Note that boost or trim only intervenes when the input voltage deviates significantly from nominal. You can examine the acceptable output voltage window by logging into the NMC and going to UPS->Power Settings. For example on a 230V unit I have here, the tightest output voltage range I can have is 207V to 253V.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

It's interesting there must be a difference between the smaller and larger units...

Looking at an old log from the 3000va unit, whilst it was just running normally shows Vmin between 235.45v and Vmax 243.35v but the output, as recorded by a different data logger, was between 240.81v - 240.95v. This is over a 24 hour period of general running of the line interactive unit. There have been some nasty power issues in that location so it was all instrumented up to look for a event. As an aside, it looks like the neutral pole of the 4 way breaker into the room was iffy causing temporary floating neutral problems and blown PSUs. It's now a 3 way breaker with a hard wired neutral

I think I'll just await the firmware for the NMC and see if an option appears, I'm sure I turned it off on the 3000va unit but it's live and a few miles away in a clients basement so I can't easily pop in and start tinkering with it. Well, until the extra battery packs turn up, then I can when add them to the units.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

you might need to change the mode to advanced (versus the default of standard). try going to the configuration menu and choosing the menu option and see if its currently set to standard and change it to advanced. then see if its under configuration or control.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
2890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

in our 6.x NMC firmware due later in December, the NMC will give you the option to toggle Green Mode on/off. today you cannot do it via the NMC. you'd have to adjust the setting via the front panel of the UPS via the LCD.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore