Smart-ups 750 rm totally dead

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-ups 750 rm totally dead
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:56 PM

0 Likes
8
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:56 PM

Smart-ups 750 rm totally dead

hi, I have a Smart-ups 750rm 2u that has been unused for about 3 years. During this time it has been disconnected from the power and with the batteries left connected. I assumed the batteries would need replacement but hoped otherwise it would work.

When I plugged it in to the power there was no reaction at all, no lights, no sound, no nothing. 

I looked for a fuse but couldn't find one. Is there anything obvious that I can try or is it ready for recycling?

cheers,

gordon

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Hi,

Yes if the LEDs are flashing in unison and resetting does not resolve the issue then the UPS need to be replaced.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:56 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:56 PM

Most APC models in this range won't power on if the batteries are completely dead. If it has been sitting for 3 years it is definitely out of warranty. You could try installing replacement batteries, but the problem is that you won't know if the problem was just the batteries or if there is something wrong with the UPS itself until you spend the money for the batteries.

Depending on the planned usage (work / home, etc.) and whether or not 750VA would be sufficient, you might want to consider replacing the unit. In addition to just recyclying the unit, APC offers the Trade-UPS program. You'd need to check to see if that would be more cost-effective than simply recycling the unit and purchasing a new unit (without trade-in) from a reseller with a good discount program. That will depend on the old and new models as well as your location.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Aah I see. Thanks very much for this information.

Do you think there is a practical possibility of charging the batteries by some other means just enough to allow the unit to start up?

It is for home use so unless I'm sure it is in working order I don't want to buy replacement batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Unlikely. I have been able to charge recently-dead batteries one at a time with a car battery charger. This is strongly NOT recommended, but it was after Hurricane Sandy and my choice was to either re-wire everything around the UPSs (or run in bypass mode on the models that support it) or to charge enough batteries to be able to start the UPSs, which would at least give me surge & sag protection (very important as the local utility stuttered and sputtered for a few days once it got going after a multi-week outage).

Batteries that have been dead for 3 years are unlikely to hold enough of a charge to allow you to start the UPS. I don't know offhand how many batteries are in your UPS or how they are configured, so I can't say what might work as an alternative. I think your best bet would be to purchase the proper replacement batteries from somewhere which will allow you to return them if they don't get your UPS going.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Thanks Terry, I'll see what I can find on ebay, or maybe give your non-recommendation a go.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

I purchased a couple of cheap batteries and installed them and the unit fired up and initially looked fine. However after a couple of hours I looked at it again and all the lights were flashing.

does this mean the batteries were too cheap?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Hi,

Are the online, on battery, bad battery, boost, trim, and overload all flashing in unison? If so there is an internal fault. If those LEDs are flashing in sequence then the unit is in sleep state.

If there is an internal fault you should brain dead / reset the UPS. Instruction on how to brain dead the UPS can be found in Kbase FA156611

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Thanks Bill - I tried that and also the cold start. However when the mains is back on the 6 lights flash again.

Does this mean there are one or more 24V relays faulty? If so does that mean the unit is ready for the bin?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

0 Likes
0
2161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:27 PM . Last Modified: ‎2024-02-29 11:55 PM

Hi,

Yes if the LEDs are flashing in unison and resetting does not resolve the issue then the UPS need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore