Smart-UPS x 3000: In Bypass: Hardware Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS x 3000: In Bypass: Hardware Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
4
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

Smart-UPS x 3000: In Bypass: Hardware Fault

This is the third device from this batch of systems we have had issues with.

What are the procedures to "Cold Start" the device again? I must have misplaced them.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

I got the log files - thanks! What I am seeing here is that the UPS battery is from 2011/2012 and your UPS has reported a battery fault and then a hot battery and it is going to bypass to stop the charging of the hot/faulty battery. To me, it sounds like you need a new battery. Have you had the chance to physically check this UPS to validate the hot battery? If not, I'd do that ASAP. It looks like you have had battery related issues for some time and that is causing the UPS to go to bypass periodically when the battery gets too hot.

I'd probably suggest contacting technical support as soon as you can with these logs to let them review it and then validate what I said and determine your warranty status.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

Coldstart just starts the UPS off of battery power and likely won't help with this. It could also cover up an issue only until it presents itself again.

Can you send the log files from your UPS to review? http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 has instructions on how to do that. We can see if we can tell what the failure is and if it is clear-able or not. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

Requested files are attached - did not look like the last post went through

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

I am working on debugging why some folks cannot upload file attachments yet I do not have a problem myself. I do not see the attachments presumably because it is not working for you either. Can you email the files to this address which will go to a Box file share I have? upload.APC_For.17z2g3olmf@u.box.com 

If it is not too much trouble, can you tell me what web browser/version and OS you're using? EDIT an adjustment was made to address file uploads. You can try again if you'd like.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:52 PM . Last Modified: ‎2024-03-06 03:08 AM

I got the log files - thanks! What I am seeing here is that the UPS battery is from 2011/2012 and your UPS has reported a battery fault and then a hot battery and it is going to bypass to stop the charging of the hot/faulty battery. To me, it sounds like you need a new battery. Have you had the chance to physically check this UPS to validate the hot battery? If not, I'd do that ASAP. It looks like you have had battery related issues for some time and that is causing the UPS to go to bypass periodically when the battery gets too hot.

I'd probably suggest contacting technical support as soon as you can with these logs to let them review it and then validate what I said and determine your warranty status.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of