Smart UPS stuck in Runtime calibration test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS stuck in Runtime calibration test
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:39 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
1
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:39 AM . Last Modified: ‎2024-02-29 10:37 PM

Smart UPS stuck in Runtime calibration test

I run a number of SMX750 UPS to support remote radio sites. I've recently added network cards to these and used the Runtime Calibration test feature. I'm assuming this test works, but the indication on the network card never goes away. There is an option to cancel the test but it has no effect. I think the test has happened and it is just the indication that has stuck, but it probably means you can't repeat the test. I've tried resetting the network card but that made no difference. So I then tried it on a spare and the test worked as expected, ran the batteries down to 25% charge, put the mains back and said test complete. I then checked software versions. The network cards are on v6.2.0 but the original UPS are on firmware UPS 03.8 (ID11) but the new one is on 09.1 (ID20). Presumably I need to upgrade the firmware of the older UPS. Has anyone come across this problem? Its quite tricky to do the firmware upgrades as the customer doesn't tolerate outages, so having to reboot all the UPS when they have been put in to avoid outages will not make me popular.

I've done some more checks and for SMX750 early hardware versions are only upgradable to 3.8. It looks like the network cards/firmware are incompatible.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

George,

We would not recommend upgrading UPS firmware except for a few specific cases. You mentioned you did a reset on the nmc's still showing this alert, do you mean you ran a reboot management interface command?  That would be my best recommendation.  Calibrations are also not recommended more often than once every 6 months as they are very taxing on the batteries.  Have you confirmed on site with the units that they are indeed working fine outside of the trial you did with one unit?

Regards,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

George,

We would not recommend upgrading UPS firmware except for a few specific cases. You mentioned you did a reset on the nmc's still showing this alert, do you mean you ran a reboot management interface command?  That would be my best recommendation.  Calibrations are also not recommended more often than once every 6 months as they are very taxing on the batteries.  Have you confirmed on site with the units that they are indeed working fine outside of the trial you did with one unit?

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of