Smart-UPS - online output power limited?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
251

Smart-UPS - online output power limited?

This question was originally posted by Alexander on APC forums on 2/24/2011


Our Smart-UPS 1000 RM is running at high capacity (around 90% load in watts) and is due to be replaced.
We suspect that load is currently (occasionally) increasing beyond 100% during heavy operations (e.g. overnight backup). We do hear the device beeping when the HP c3000 BladeSystem is booted.

Question 1) Is output power on these devices limited when running on-line (i.e. not on battery)? For example, if the connected equipment were to demand 1500, will the Smart-UPS deliver, or will the connected devices be 'starved' of current? This could explain unexpected shutdown behaviour on one of the server blades.

Question 2) This cabinet is almost full and we don't envisage adding much more equipment - maybe another 500 VA max. Would 2000 VA be the next logical step - or 3000 VA?

Thanks!

Attachments
Tags (3)

Accepted Solutions
Elec_apc
Ensign
Ensign
0 Likes
0
251

Re: Smart-UPS - online output power limited?

This was originally posted on APC forums on 2/24/2011


In my advice it will be better to replace a ups with 3000 va capacity , because you have 1500 va load this mean 50% of load capacity for (3 kva unit),
it is always better that run a unit at half load,and take in consideration that you have always a peak current consumed by server equipment at start up, this peak current
can cause an overload for small sized unit.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
251

Re: Smart-UPS - online output power limited?

This reply was originally posted by Alexander on APC forums on 2/28/2011


Thanks for the answers. We'll replace with a 3000VA.

Elec_apc
Ensign
Ensign
0 Likes
0
251

Re: Smart-UPS - online output power limited?

This was originally posted on APC forums on 2/28/2011


Welcome

Elec_apc
Ensign
Ensign
0 Likes
0
252

Re: Smart-UPS - online output power limited?

This was originally posted on APC forums on 2/24/2011


In my advice it will be better to replace a ups with 3000 va capacity , because you have 1500 va load this mean 50% of load capacity for (3 kva unit),
it is always better that run a unit at half load,and take in consideration that you have always a peak current consumed by server equipment at start up, this peak current
can cause an overload for small sized unit.