Smart UPS 1000 RM batteries show signs of melting bubbling

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1000 RM batteries show signs of melting bubbling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:46 AM

0 Likes
4
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:46 AM

Smart UPS 1000 RM batteries show signs of melting bubbling

A few days ago my Smart UPS 1000RM (the unit was purchased in January of 2008 and installed at that time) indicated that the batteries (original) needed to be replaced, I ordered new batteries and went to replace them yesterday. After struggling to get the old batteries out, I noticed that two of the four batteries show signs of melting and/or bubbling. This was the reason as to why the batteries simply didn't slide out. I have a few questions regarding this.

Why wasn't I notified before this point? All of my units are monitored by the Powerchute Business deluxe edition software package.

What is the worse case scenario regarding these batteries?

Is there a battery life limit regardless of operating condition?

I have around 20 additional Smart UPS APC units which include various models (bigger and smaller) should I be physically checking the conditions of those batteries?

Thank you in advance for any comments regarding this.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • bubbling
  • melting
  • PowerChute
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:46 AM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:46 AM

I have seen many cases of those battery in apc unit and replaced them with new one and units continue to work normally,
first note that this problem is not caused by apc unit, here are some reason why battery bubble in this way:
the battery used inside apc unit are lead acid battery and it contain a little percent of acid, if the battery is heated than the acid will evaporate and need to go out of
the battery this way it will bubble.
there are 2 reason for battery heating:
first bad environmental,the room temperature is high ,or the battery are not ventilated properly.
second when battery ages it will be internally defected than it will not reach its floating charging voltage in the proper time ,for this reason the charger will take much more time charging the battery and some times will not stop,this will heat up the battery over time.
for this reason some fan of units will rotate more than the normal time.

to prevent this problem ventilate properly the units with good environmental ; and always calibrate the ups from powerchute software if you notice that runtime is very low after calibration this mean battery are bad and must be changed before it bubbles.

Reply

Link copied. Please paste this link to share this article on your social media post.

Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

Jeffswan, when was the last time you did a runtime calibration with your old batteries? Probably never? If so then the self-tests having been lying to you for a while now, and capacity has been significantly less than what powerchute was reporting.

Don't worry about it, you learn to get used to the fact that self-testing is only good for testing the period of time the test actually runs, and is not a useful indicator of run-time for any longer than that.

,

Elec, the bulging can be from overcharging/overheating but also from sulfation of the lead oxide plates. The oxide forms pure crystals that don't dissolve when recharged, and the crystals grow bigger and bigger until they start touching plates together, shorting out a cell.

The crystals are capable of significant physical pressure on surrounding objects as they grow in size, and that is what makes the plastic case bulge out. Inside the plates are being pushed around and bent/damaged by the crystals.

It's just how it is with battery technology. Pure crystal formation affects pretty much all chemistry types, like NiCd.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

ok man good details about battery thank.s

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:14 AM . Last Modified: ‎2024-03-08 04:45 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore