Smart UPS doesn't follow delayed turn on schedule on power restore

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS doesn't follow delayed turn on schedule on power restore
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
6
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Smart UPS doesn't follow delayed turn on schedule on power restore

I have a Smart UPS (SMX3000LV).  I have it configured to do a staggered power on of the 3 outlet groups to allow a controlled startup of all the connected networking equipment, file server, and other servers.  This works nicely on initial power up.

Here is my problem.

  • On power failure, the connected server directs the UPS to shutdown
    • this also works nicely, and the UPS goes into a mode where it says "Waiting for AC" on the display.
  • When power is restored, the UPS turns back on...
    • BUT... instead of following the specific delayed turn on that is programmed for each outlet group, it just turns them all on immediately!
    • There is nothing in the menus on the UPS that talks about a restart delay, or gives me anything else to program.

Is there something I'm missing in the configuration that tells the UPS to ignore it's programmed power on delays on restart?

Why is this behavior even possible... the delays are programmed for a reason, why would it ever ignore them on power-on?

Thanks in advance for any insight the forum might have.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

Thanks for sharing your thoughts on this Bill.  I don't have the network card.  I didn't buy it because it wasn't likely to be supported by my linux platform.

The linux server that is actually directly connected to the UPS is a "FreeNAS" installation.  This is a version of FreeBSD that is specifically built to be a file server (think NetApp).  The build is very thin, and everything is set up via a GUI on a webpage.  It is extremely robust and powerful, but you don't want to deviate from what can be achieved in the GUI or it becomes very hard to maintain.

Using NUT, because it's a supported built-in function of FreeNAS, is a mandatory starting point for my environment.  It's also nice that the NUT clients are available for just about every platform so I can put any type of machine on the UPS and slave it's behavior, via NUT, to the computer controlling the UPS shutdowns.

I'm happy enough with the solution I sorted out.  I just wanted to comment here to talk about the behavior of the UPS to encourage APC to make the behavior more standard going forward and follow the power-on delays under all circumstance where the outlets go from off to on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:22 AM

Hi,

Are you configuring a power on delay for outlet under sequencing or min return runtime? Also, how is the UPS being commanded off? 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:22 AM

The delay was actually programmed as a "Power On Delay", but it was programmed (initially) from the front panel of the UPS, not from the powerchute software.  "Min return runtime" is used, as I understand it, to set the amount of charge the batteries must have before the UPS will power the outlet group back on.

The UPS is being commanded off by the usbhid-ups driver from NUT (network UPS Tools) in Linux.  This is how it reaches the "Waiting for AC" state where the LEDs sequence back and forth.

When I connect the UPS to a windows computer running powerchute business edition agent/server/console, I can see all the configuration that was made on the front panel.  In this case, when shutdown is initiated, it seems to "sleep" in a different state where it says "Outlet Group 2 on by USB in: 120s", and just sits there waiting for AC power.  When AC power returns, the 120s starts counting down, and it does a properly sequenced power up.

So... using powerchute, the behavior is as desired.  Unfortunately, I have a rack of linux machines that need to be controlled (not just one machine), and powerchute for business on Linux doesn't appear to have a USB option.  I'll explore this more closely.  Everything I have natively runs NUT.  Not all of the machines will be able to run powerchute.

So this question boils down to... On the SMX3000LV, when it reaches the "Waiting on AC" sleep state, why does it not follow the power-on delays when AC power returns?  How do I alter that behavior?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

Hi,

You can verify the UPS is working properly by configuring load shedding on the outlet group and have a power on delay set. Example under Configuration for Group1 set the power on delay for 120  Loadshed: Time on Battery: Enabled, Loadshed: Time on Battery: 120. 

What should happen is when the UPS goes on battery after 120 seconds the outlet group will be powered off. When AC is restored the outlet group will wait 120 seconds and then restore power to the outlet group. If the UPS works as expected than the issue is with the shutdown command NUT is using. Unfortunately I am not familiar with NUT but if there is a users group for that app or a forum they may be able to help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

Since the process works correctly with PowerChute, the issue is indeed with the command issue by NUT... or more specifically, the response my UPS has to the command that is issued by NUT.  I can argue that there is a bug in the firmware of the UPS that is allowing the UPS to power on its outlets, ignoring the power on delays that are programmed into the UPS, when AC is restored.

Since I don't expect a fix, either from the USB driver in NUT or the firmware of the UPS, I've changed my setup to remove the power on delays and instead allow everything to power up simultaneously and I handle the staggering of boot times in software on the respective machines.  Not as elegant, but it is functional and possibly more robust as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

Russ,

If your SMX3000 has a network management card and if the Linux version is supported you have the option of installing PowerChute Network Shutdown. You would then configure the shutdown and start up via the outlet groups. This way you can use the delays set at the UPS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

0 Likes
0
2419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:11 PM . Last Modified: ‎2024-03-06 03:22 AM

Thanks for sharing your thoughts on this Bill.  I don't have the network card.  I didn't buy it because it wasn't likely to be supported by my linux platform.

The linux server that is actually directly connected to the UPS is a "FreeNAS" installation.  This is a version of FreeBSD that is specifically built to be a file server (think NetApp).  The build is very thin, and everything is set up via a GUI on a webpage.  It is extremely robust and powerful, but you don't want to deviate from what can be achieved in the GUI or it becomes very hard to maintain.

Using NUT, because it's a supported built-in function of FreeNAS, is a mandatory starting point for my environment.  It's also nice that the NUT clients are available for just about every platform so I can put any type of machine on the UPS and slave it's behavior, via NUT, to the computer controlling the UPS shutdowns.

I'm happy enough with the solution I sorted out.  I just wanted to comment here to talk about the behavior of the UPS to encourage APC to make the behavior more standard going forward and follow the power-on delays under all circumstance where the outlets go from off to on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of