Battery Fault after configuring External Battery Cabinet Capacity

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery Fault after configuring External Battery Cabinet Capacity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
7
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Battery Fault after configuring External Battery Cabinet Capacity

Hello!

I currently operate two Smart-UPS 20Kva units, both have an extra XLBP connected. They have been running since since last year with no issues. Last week, i noticed that the "External Battery Cabinet" field was empty, so i searched for the AMP-Hour capacity of the XLBP(3840 per the documentation) and configured it on both devices. After that i ran a run time calibration on both devices, and the runtime almost doubled, which is great. The weird part is that both devices reported a battery fault, this has never happened before. Did i configure something wrong? Both devices were installed in March '14, and both run at 5~20% load, never higher. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • runtime
  • surt20kva
  • xlbp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Then what i did was wrong, now i'm curious here, when should i populate the "External Battery Cabinet:  Amp-Hour" field, and what information goes in there? Does it even apply to my devices? 

Thank you Bill for taking your time to answer!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Hi,

Please provide the full model numbers of the Smart-UPS and the external battery packs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Hello Bill,

UPS model: Smart-UPS RT 20kVA RM 230V SURT20KRMXLI

Battery Pack: SURT192RMXLBP2

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Hi,

The battery packs are intelligent so the UPS should say "Batteries increased" on the screen when they are attached. If there is an error you should run a self-test to see if the error clears. If the error does not clear it is possible one of the batteries need to be replaced and you should contact local support for assistance. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Bill,

I can't recall if we actually saw a message like that, but if the batteries are in fact intelligent, they should have been noticed by the UPS. Thing is, i should be seeing 16 batteries and not 8, but thats what i'm getting on both the units i have. Is this correct?

Battery
Capacity: 100.0 %
Nominal Battery Voltage: 192.0 VDC
Actual Battery Bus Voltage: 218.9 VDC
Battery Current: +0000.1 Amps
Batteries: 8

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Hi,

The batteries are smart and should be discovered by the UPS when connected. It can take 2 - 4  minutes to auto discover. If they do not then the connector is not full engaged. 

The battery number is correct. There are 4 sets of 2 battery packs in a series per cabinet so with 2 cabinets the total is 8 batteries. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

That is where it got confusing, there are 8 RBCs on each battery encasing, but they are accounted as four batteries per case then? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:10 PM . Last Modified: ‎2024-03-06 03:23 AM

Then what i did was wrong, now i'm curious here, when should i populate the "External Battery Cabinet:  Amp-Hour" field, and what information goes in there? Does it even apply to my devices? 

Thank you Bill for taking your time to answer!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore