I am setting up some Smart UPSs.
I have them connected with USB to the servers.
I've set one server i.e. to initiate shut-down after 30s on battery. This server is on outlet group 1.
I've then set the Outlet Group 1 as follows:
turn on delay: 0s
turn off delay: 150s (server needs around 90s to shutdown)
reboot duration: 8s
loadshed on battery: enabled
loadshed: 30s
So, it should wait 30 before going to turn off delay. then wait 150s and then turn off the power.
What it does it after 30s it turns the power off.
What am I configuring wrong?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:20 PM . Last Modified: 2024-03-19 12:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:20 PM . Last Modified: 2024-03-19 12:11 AM
Jordan,
Thank you for your reply.
I thought that after the load shed time it would wait another 150s to turn-off.
Isn't this the turn off delay?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:20 PM . Last Modified: 2024-03-19 12:11 AM
Anthony,
I believe this may have do to with the load shed you have enabled and configured for 30 seconds on group 1. Have you tried disabling load shed?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:20 PM . Last Modified: 2024-03-19 12:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:20 PM . Last Modified: 2024-03-19 12:11 AM
Jordan,
Thank you for your reply.
I thought that after the load shed time it would wait another 150s to turn-off.
Isn't this the turn off delay?
Link copied. Please paste this link to share this article on your social media post.