Smart-UPS XL 1000 + APC UXBP24 - Battery backup time Inconsistency

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS XL 1000 + APC UXBP24 - Battery backup time Inconsistency
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
12
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

Smart-UPS XL 1000 + APC UXBP24 - Battery backup time Inconsistency

Hi,

I am using the above mentioned devices as backup power for 4 PCs (4 CPUs + 4 Monitors). I am having a problem which I am not able to understand why, so can some one please give me a solution or an explanation.

Whenever I do a calibration testing through the APC Business chute client to check the backup time for the UPS with the battery pack I get a battery time of little over 7 hours, I know the UPS is drawing power from the battery during this test, because the UPS indicated that it running on battery and the UPS fan is on.

But when I pull the power cord for the APC from the AC supply and make it run on the battery the backup time is little less than 3 hours.

Can some one give me an explanation or how I could get a consistent result.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

If you don't even get "SM" then there's either something wrong with the serial port, or the procedure was done incorrectly.

By already communicating with PCBE you've verified that it can communicate using the Comm board on the UPS, just right now, by USB.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

Yes the battery count is set for 5. These units are brand new, 4 months old. The UPS is the APC SMART-UPS 1000XL with the UXBP24 battery pack.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

Suhan,

I'll assume you're currently using USB since you're asking if there's a difference. If you can do the following with some downtime, we can test for sure:

1. Power off all attached load
2. Power off UPS and disconnect from the wall.
3. Disconnect the communication cable
4. Depress the Off button for 4-6 seconds until you hear a click and the front LED's flash.
5. Hook the serial cable up and re-attach the load and power everything up.

Now, open up Hyperterminal (2400/8/n/1 No Flow Control)
Press Shift+Y (should return "SM")
Press Shift+(Period) (Should return "005")
If it does not, let me know.

Also at this point you may want to reinstall the Agent because you're on Serial communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

Hi,

I will not be able to test this out, because the computers that are connected be taken down right now. I will have to perform this test some time tomorrow morning or later on Friday.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

In the PCBE interface for the device, do you have "005" for the Battery Pack Count? When was the last time the internal batteries were replaced? What's the full model number of the UPS that you are using? It's possible you'll need to contact Tech Support and request a calibration key be sent to you if it is an older model.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

Hi,

When you do the pull plug, do you have anything that's setup with PCBE to perform a shutdown at all? Shutting down after 50% of battery life, when you initially have a "7-hour" runtime and your equipment/UPS is powering off after half that time, there's either a large shutdown schedule, or an extremely non-linear load that's increasing as the UPS operates on battery. What exactly is connected to the UPS? If it's a Server/PC, does it contain a Power Factor Corrected Power Supply?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

"do you have anything that's setup with PCBE to perform a shutdown at all?" I am not clear as to what do you mean anything setup in PCBE, could you elaborate this please ?

I don't think I have any kind of shut down scheduled in the PCBE.

After the calibration test I let the UPS power back to full before I do the pull plug option. I only have 4 Desktop CPUs (no servers) and 4 17" LCD monitors connected to the UPS. I am not sure if the power supplies are PFC power supplies, but these machines are fairly new, so I am assuming they are.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

In regards to what you asked for clarification on - it's not important. If you had something setup for a shutdown on battery after X minutes, you would've known right away.

Anyways...4PC's and 4 Monitors...on a UPS that's only capable of a maximum of 800Watts. What is your load percentage during normal operation? It has to be EXTREMELY close to 800W, or at least within 100W of an overload.

If they are power factor corrected power supplies and you're SOMEHOW avoiding an overload condition on battery, your runtime is extremely skewed based on the PFC PSU's.

What's happening is that during the transfer time from online to on battery there are capacitors in the PFC PSU that immediately drain to keep the system up and running for that 2-4 Millisecond time. Once the UPS is on battery, the capacitors decide they want to do a full recharge immediately, which increases the power draw on the UPS substantially (here's where it SHOULD be overloading), and decreasing your runtime substantially.

When you do the pull plug, do you watch the software and actually see the runtime decreasing, then @ 3 hours it just turns off?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:36 AM

The load percentage at normal operation with all 4 computers connected is at 2 LED Bars. Also do keep in mind I have the extra battery pack connected as well.

When I pull the plug, the LED bars keep dropping at regular interval and once it comes to the end all the devices just shut off. I also check on the software which shows what the percentage is as it is dropping.

According to you, is there a way I can prevent the overloading phase. So why am I not affected by the overloading problem when I am doing the calibration. Shouldn't this happen during then as well ?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

Keep in mind that an extra battery does not increase load capacity, only runtime.

Do you have the specifications on the Power Supplies for the PC's? Based on the information the UPS is reporting to you, it's providing around 44% load power with 8 devices attached to it, 4 of which are PC's, meaning that it's 44% of 800VA, or roughly 365VA. Still doesn't seem like the UPS is correctly sensing the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

Hey,

The 4 PC's have a 350 W power supply each.

Another question, when I am setting the battery pack value on the BCE, does it matter if I use a USB cable or Serial Cable. Also does setting the battery pack value on the software client make the UPS recognize the extra battery pack, if so how can I make sure ?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

Hi,

I will not be able to do this test for another week or so, so let me ask you, what I could do if I do not get "SM" and "5", during this test ?

How can I go about making the UPS recognize the battery pack ?

Thank You

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:25 AM . Last Modified: ‎2024-03-08 02:35 AM

If you don't even get "SM" then there's either something wrong with the serial port, or the procedure was done incorrectly.

By already communicating with PCBE you've verified that it can communicate using the Comm board on the UPS, just right now, by USB.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of