Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS X 3000 was still compensating the power output after the voltage has gone back normal

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000 was still compensating the power output after the voltage has gone back normal
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
5
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

Smart-UPS X 3000 was still compensating the power output after the voltage has gone back normal

My company owns  Smart-UPS X 3000.

One of the UPS showed an error "UPS: Compensating for a low input voltage.".

But after 20 minutes, it still shows that it has a poor input and was still compensating the power output. We looked at the input voltage and frequency. They are just normal and within the range between output upper limit and lower limit.

Is it by design? It stopped just after we manually perform UPS self-test. When would it stop automatically?

And for the option "Sensitivity", is it related?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

I'm not sure where it's documented.

The idea is when the voltage is moving around the limit, the UPS designers want to avoid the UPS switching rapidly in and out of compensation. So say the upper limit is 260 V and there's 2V of hysteresis, it'll start compensating at 260 and will remain in compensation until voltage drops below 260-2 => 258V. You can determine the hysteresis amount experimentally using a variac.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

Hi,

The UPS should have switched over automatically. Running the self-test or resetting the UPS was the proper solution. 

On 5/26/2016 10:33 PM, H said:

And for the option "Sensitivity", is it related?

For information on Sensitivity please review Knowledge Base document FA156514 "What are the different sensitivity settings of a Smart-UPS?"

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

Running the self-test or resetting the UPS was the proper solution. 

It sounds very odd to me that if this occurs at night or in holidays, the UPS will be in compensation mode for a long time.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

If the input is still near the limits, the UPS will continue to compensate due to hysteresis.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

Thanks! Is there any manual talking about this kind of hysteresis? i.e. the formula or decision tree for the UPS to judge whether it still needs to compensate? 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:13 PM . Last Modified: ‎2024-03-06 11:19 PM

I'm not sure where it's documented.

The idea is when the voltage is moving around the limit, the UPS designers want to avoid the UPS switching rapidly in and out of compensation. So say the upper limit is 260 V and there's 2V of hysteresis, it'll start compensating at 260 and will remain in compensation until voltage drops below 260-2 => 258V. You can determine the hysteresis amount experimentally using a variac.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore