Smart UPS SUA750 completly dead, wont even power up. please help

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS Data Center & Enterprise Solutions Forum
            • Re: Smart UPS SUA750 completly dead, wont even power up. please help
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            5060
            voidstar_apc
            Janeway voidstar_apc
            196
            Teken
            Spock Teken
            136
            Erasmus_apc
            Sisko Erasmus_apc
            112
            View All

            Free

            English

            Data Center Certified Associate Exam Development Path

            Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

            4.0
            Register Browse SE University

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Solved Go to Solution
            Back to APC UPS Data Center & Enterprise Solutions Forum
            Start a Topic
            Solved
            Anonymous user
            Not applicable

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            7
            2265
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            Smart UPS SUA750 completly dead, wont even power up. please help

            I bought a SUA750 about 2.5 years ago to protect my home theater projector. about 6 months ago or so (after a few brownouts) it started telling me the batteries needed replacing. I got busy and temporarily removed bypassed the UPS and pluged my projector directly into the wall with just a surge protector. I turned off the UPS and just left it there plugged in for 5-6 months. Now that i decided to finally replace the batteries, i went to power the thing up, and its completely dead. I get no response when i push the power button on the front of the unit. I am an electronics engineer so I'm not afraid to open the thing up and poke around inside. I did so and found that the mains power to the board looks fine, I followed the wires to see where they attached to the main pcb and then measured using a multimeter. The voltage looked fine at 120V. However the Battery voltage is very low like 2.5V or so. Any ideas at what to try next? Id rather not have to drop another 200-250$ on a new one when the thing isn't that old. Is there any fuses that could have broke (besides the overload protection, its between the cord and the pcb so it seems ok since i get voltage at the pcb)? I also checked the front buttons and verified that they work as they should.

            Any help would be greatly appreciated.

            Labels
            • Labels:
            • Smart-UPS & Symmetra LX | RM
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic

            Accepted Solutions
            Anonymous user
            Not applicable

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            I believe what they mean is that they hooked up the DC voltage to where the batteries would usually be connected and the unit was able to turn on.

            I just recycled a 750 unit that was completely non responsive and I put new batteries and it turned right on.

            The existing batteries were at less than 1v and as a result caused the system to not turn on at all.

            Luckily I have a pile of spare 12v batteries to test with. 

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Replies 7
            voidstar_apc
            Janeway voidstar_apc
            Janeway

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            Did you replace the battery with a charged battery? After 5 or 6 months, the existing one is almost certainly dead. Without the battery, it lacks the power needed to run the UPS.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            Next week at work i'll try hooking up the battery terminals to a DC power supply and try powering it up with out the AC plugged in. If that works then i trust that it is fine, and i just need new batteries. So can anyone verify that these units don't work at all without batteries/don't even power up at all even after being plugged in for a long time (over night). I thought that you could run them without batteries and they would just act as a surge suppressor/ power conditioner just fine?

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            i have tested this and an SUA750 should power up by itself without a good battery but the UPS would flash the replace battery LED at you telling you that the battery is not connected/isnt detected.

            on the older Smart UPS, beginning with SU (such as SU700), they would show no sign of life at all besides the very first time you tried to turn it on. it would flash and beep quickly and thats it.

            i believe that the UPS should at least beep at you/flash the replace battery LED. i will double check this in the morning when I can test it to be 100% sure.

            any UPS that APC makes, in general, can be used without a battery but will beep/flash at you that the battery is missing. then, during a power outage of course, it will turn off.

            i'll post back after testing it myself since i did that several months ago. i am second guessing myself after voidstar's reply.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            voidstar_apc
            Janeway voidstar_apc
            Janeway

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            I'm guessing the manual meant that the unit will continue to run while the battery is disconnected so that the battery can be replaced, not that it can start up without a battery. Especially since you've shown that it can't.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            Hi, I have a SUA1500I that shows the exact same symptoms: after sitting unplugged for several months (it told me I had to replace the battery pack), the battery only has ~9V and the UPS doesn't power on, with or without the battery. I've read somewhere that some models don't power up without a battery but the manual says it should work if the battery is removed. Can anyone tell us if that is correct only if the UPS was running prior to the removal of the battery? Maybe models from different generations behave differently?
            Please help!

            PS: after reading this thread http://forums.isxusergroups.com/thread.jspa?threadID=1772&tstart=210 , I took my laptop AC adapter and charged the capacitors. It really did the trick! My SUA1500I powered on so now I have a reason to buy a new bat. pack!

            Message was edited by: tzobor

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2264
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            Hopefully you get this.  Any chance you remember what you did to revive your UPS using the laptop AC adapter?  The website you referenced doesn't exist any longer so I can't see what was done and I think mine suffers from the same issue.

            Thanks!

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            0 Likes
            0
            2265
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-30 05:14 AM . Last Modified: ‎2024-03-08 02:59 AM

            I believe what they mean is that they hooked up the DC voltage to where the batteries would usually be connected and the unit was able to turn on.

            I just recycled a 750 unit that was completely non responsive and I put new batteries and it turned right on.

            The existing batteries were at less than 1v and as a result caused the system to not turn on at all.

            Luckily I have a pile of spare 12v batteries to test with. 

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Preview Exit Preview

            Photos

            • Upload Upload
            • URL URL
            • Saved Photos Saved Photos
            Upload location
            • Add Photos to Album:
            • New Album
            • Upload location
              • Add Photos to Album:
              • New Album
              Drag here to start uploading
              Drag photos here or
              Tap for upload options
              You must install or upgrade to the latest version of Adobe Flash Player before you can upload images.
            Photos

            never-displayed

            You must be signed in to add attachments

            never-displayed

             

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.