Hey everyone!
I just acquired a 3000RMXL for the office, however it is using a L5-30P plug, which we currently do not have a receptacle for. Would it be acceptable to just purchase a 30A to 15A converter (straight blade receptacle)? Suggestions? Else, call the electrician. =P
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:14 AM . Last Modified: 2024-03-08 02:59 AM
hi,
[check this link out|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]
it should answer your questions. as the article notes, you can but it will de-rate the UPS. you will need to make sure you dont overload it and trip the breaker.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:14 AM . Last Modified: 2024-03-08 02:59 AM
hi,
[check this link out|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]
it should answer your questions. as the article notes, you can but it will de-rate the UPS. you will need to make sure you dont overload it and trip the breaker.