Smart-UPS SUA2200 too high float voltage damaging batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SUA2200 too high float voltage damaging batteries
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
5
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

Smart-UPS SUA2200 too high float voltage damaging batteries

I have an old Smart UPS SUA2200XL. ES963316251 Manufacture Date 10/8/1996. I know it is an old unit, but it works great still.

But, after 8years of the same batteries, they died. They all got swollen and when I replaced the batteries, I was advised to check the float voltage for possible overcharging issues once the batteries reach full charge. With the new installed batteries, I recalibrated the UPS by letting the power cycle to discharge, recharged then ran the battery run-time calibration.

Now, I look at the battery status and it indicates the battery voltage is 56.15 VDC, and verified this with a DMM at the terminals. I've read a few posts and from what I read, the float voltage should be in the range of 54.5- 54.8 volts.

Isnt this too high and could this be a cause of premature failure of batteries? Has anyone succesfully reduced the float voltage? I have heard there is a capacity that generally fails causing this?

What is interesting is that in the course of debugging an earlier problem with the battery showing discharge state, (which I solved), I measured battery voltage after first installing new batteries, and that time, and it was 51 - 51.4v, which is a low float voltage. I then pulled the batteries to check the connections, and to make sure the terminals were solid, and re-installed, and ran all the calibrations, and then the unit was working, but the voltage increased to 56v. Which implies this is not a hardware problem, as I know these units can have faulty capacitors over time that cause this, and suggests some sort of calibration will fix the problem.

Michael

I attached a word file with my UPS Stats

Agent version 9.0.0.613.

Message was edited by: hatzakis

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

Yes, of course I did. Please see my comments over there as well... thank you..! Michael

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

I have an old Smart UPS SUA2200XL. ES963316251 Manufacture Date 10/8/1996. I know it is an old unit, but it works great still.

But, after 8years of the same batteries, they died. They all got swollen and when I replaced the batteries, I was advised to check the float voltage for possible overcharging issues once the batteries reach full charge. With the new installed batteries, I recalibrated the UPS by letting the power cycle to discharge, recharged then ran the battery run-time calibration.

Now, I look at the battery status and it indicates the battery voltage is 56.15 VDC, and verified this with a DMM at the terminals. I've read a few posts and from what I read, the float voltage should be in the range of 54.5- 54.8 volts.

Isnt this too high and could this be a cause of premature failure of batteries? Has anyone succesfully reduced the float voltage? I have heard there is a capacity that generally fails causing this?

What is interesting is that in the course of debugging an earlier problem with the battery showing discharge state, (which I solved), I measured battery voltage after first installing new batteries, and that time, and it was 51 - 51.4v, which is a low float voltage. I then pulled the batteries to check the connections, and to make sure the terminals were solid, and re-installed, and ran all the calibrations, and then the unit was working, but the voltage increased to 56v. Which implies this is not a hardware problem, as I know these units can have faulty capacitors over time that cause this, and suggests some sort of calibration will fix the problem.

Michael

I attached a word file with my UPS Stats

Agent version 9.0.0.613.

Message was edited by: hatzakis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

yeah i posted too on the other thread..the unit is older and we have made several adjustments since then to the hardware platforms. i am not sure what specifics you'd need to adjust upon opening the unit but we cannot advise you to do that. if you got 8 years out of the batteries, that is a lot more from the typical 3-5 year lifetime though and maybe there isn't an issue here..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

No, is has not gone down since I posted. I did a calibration and although the load was only at 20%, I read that one should not do more than one per year as the deep discharge is not good for the DLA batteries.

So, the question is, with too high a float voltage, and the type of failure., ie, most batteries being open (electrically) and swollen, makes me think this problem may have been going on for some time, ie., too high float, increased temperature causing them to swell. I don't have the money to upgrade just yet, I want to trade up to the new SU2200, but I have concerns that this design problem may not have been solved as I have seen many others online that report the same problem, some going as far as using a terminal interface to try to change the battery voltage gain.

How would I reduce the float voltage? Is there a way to recalibrate in another way besides what I did? Ie., I know this is probably proprietary, but I know there are commands one can use to program the UPS in ways the Powerchute cannot. Is there a program that can be run to do this?

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

http://forums.apc.com/spaces/11/netbotz-hardware-software/forums/general/1186/modem-with-rackbotz-40...

you posted on this one

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:34 AM

Yes, of course I did. Please see my comments over there as well... thank you..! Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of