Smart-UPS SUA1500 not detected by powerchute

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SUA1500 not detected by powerchute
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:26 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
12
8415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:26 AM . Last Modified: ‎2024-03-18 04:39 AM

Smart-UPS SUA1500 not detected by powerchute

We've recently bought a new server (a brand new Dell Poweredge) and are running server 2008. The problem we have is that we can't get Powerchute business version 9 (the latest version on the APC site) to detect the UPS and allow the agent to install.

The UPS has an USB socket and is connected directly to the server by a standard USB cable.

The UPS is detected by windows (there's an APC UPS HID device, and either a HID UPS battery or APC UPS detected in device manager) and we can control the basic shutdown features from within windows, however we simply can't get the agent to install as it cannot detect the UPS. Our previous server ran server 2003 and powerchute version 8 and worked perfectly. Unfortunately we can't find the original install disc for the UPS.

Is there anything we can do to force powerchute setup to detect the UPS? Are there different versions of powerchute for Windows server x64?

For reference:

UPS Model no: SUA1500 I or L (the label is unclear)

serial no: AS1033111775

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi,

A SUA1500i should have a serial port in the upper left of the back plate. 

To install without auto detect, when you execute the installer (double click pcbesetup.exe then click setup, do not close the window) the install files are uncompressed to the system default temp folder. To find the system temp folder right click on my computer, select properties, advanced system settings, environment variables. Under User variables for User Name you will find the path to the system default temp folder.

 

In the temp folder you will find a folder with a name similar to WZSE2.TMP

When you open that folder you will find PowerChute files and you need to open the Bin folder. 

In the Bin folder for your unit you would open agent-upslink and launch the setup.exe from there. 

When running setup.exe do not auto detect the UPS. Enter USB as the communication port and Smart-UPS and the UPS type. 

I apologize. I pointed out the age of the UPS not because I thought the age was a contributing factor but because I mistakenly read the post. I was thinking you wrote the UPS was new when in fact you wrote the Server was new. Again, I apologize for the confusion. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Thanks for the help Bill. I discovered that the Agent service was not starting during the installation but timing out. After several tries, waiting over a minute the service eventually started OK and everything seems to be functioning correctly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi,

This may be caused by an issue with the USB controller firmware that causes it to reset if it receives more than 8 bytes of data.

You can attempt to install PowerChute and not use auto-detect. Run the installer and select DB 9 at the manual UPS selection. Then when asked to automatically search all communication ports for UPS select No. At UPS type select Smart-UPS and for communication port select USB. If after doing that the UPS and system still do not communicate you should uninstall, brain dead the UPS (see Kbase FA156611) then connect via Serial and run the PowerChute installer. If a Serial port is not available you can use a USB to Serial converter to install and communicate serially. 

FYI: The serial number of the UPS indicates the unit is 5 1/2 years old and the model number includes the letter I as in India. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Thanks Bill. The problem with trying to install manually is that the powerchute agent installer cannot detect the UPS during setup and will not load. The SUA1500I we have only has an USB connection (rather than serial) so it looks like we'll be stuck with using the built in Windows Server power management (which is no bad thing, the problem is we lose the UPS management tools).

As for the UPS' age, it is an old unit, but has recently had a new battery pack so we won't be changing it for some time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi,

A SUA1500i should have a serial port in the upper left of the back plate. 

To install without auto detect, when you execute the installer (double click pcbesetup.exe then click setup, do not close the window) the install files are uncompressed to the system default temp folder. To find the system temp folder right click on my computer, select properties, advanced system settings, environment variables. Under User variables for User Name you will find the path to the system default temp folder.

 

In the temp folder you will find a folder with a name similar to WZSE2.TMP

When you open that folder you will find PowerChute files and you need to open the Bin folder. 

In the Bin folder for your unit you would open agent-upslink and launch the setup.exe from there. 

When running setup.exe do not auto detect the UPS. Enter USB as the communication port and Smart-UPS and the UPS type. 

I apologize. I pointed out the age of the UPS not because I thought the age was a contributing factor but because I mistakenly read the post. I was thinking you wrote the UPS was new when in fact you wrote the Server was new. Again, I apologize for the confusion. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Thanks for that post Bill. After following those instructions to the letter we now have the powerchute agent loaded on the system with no problems

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi, I am having an identical problem with the same model of Smart-UPS which I have rejuvenated with a new battery. I am using it on my home Desktop system which I have upgraded to Windows 10. I am trying to install PowerChute Personal Edition version 3.0.2, but it stalls with the information that it is unable to locate a battery backup system. The USB connection (direct to the PC) is working and Windows detects an HID UPS Battery. How can I get PowerChute to do the same??

I have tried to follow your instructions but I think the Personal Edition of PowerChute must work a bit differently as I can't see how to do it.

  • Tags:
  • installation
  • PowerChute
  • problem
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

The only advice I can give is for you to make sure the version of powerchute personal you're using is set to use upslink as the communication protocol.
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi Andrew,

PowerChute Personal Edition only works on our BackUPS products. You want to install the free PowerChute Business Edition which works with our SmartUPS units.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

On 3/11/2016 3:34 PM, voidstar said:

PowerChute Personal Edition only works on our BackUPS products. You want to install the free PowerChute Business Edition which works with our SmartUPS units.

Hope that helps

Thanks voidstar, I have tried your suggestion but the installation is way too complex and I can't get it to work at all. It appears to identify my UPS during the install but comes up empty when finished. I am absolutely certain that I used a much simpler version when I first installed on my old PC waaay back. Do I need to install all three apps since I am only controlling one UPS? I tried only installing the Agent, but could not get it to do anything. With all 3 apps installed the server doesn't seem to see the agent and vice versa.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Andrew,

You only need to install the Agent. To access the Agent once install launch a web browser I.E., Firefox, Chrome. In the address bar enter https://127.0.0.1:6547 The Agent will be accessible. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Thanks for the help Bill. I discovered that the Agent service was not starting during the installation but timing out. After several tries, waiting over a minute the service eventually started OK and everything seems to be functioning correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hello,

Is the guide above for Windows Server or Windows 10?  When I navigate to the temp folder, I don't see the bin folder.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

0 Likes
0
8413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:27 AM . Last Modified: ‎2024-03-18 04:39 AM

Hi,

Are you installing the latest version of PowerChute Business Edition. That is version 9.5 and the files will be found in the Agent folder. The path would be similar to C:\Users\UserName\AppData\Temp\WZSE0.TMP\agent

W%2B0hJCTDD9YkAlbZrpV5RA%3D%3D.pngW%2B0hJCTDD9YkAlbZrpV5RA%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore