Question regaurding Overload/Max Amps

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Question regaurding Overload/Max Amps
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
115
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

0 Likes
7
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

Question regaurding Overload/Max Amps

Hi there,

First i wanted to say thanks. This forum has always provided me with good information.. so good work πŸ™‚

On to the issue at hand. In regarding to PDU AP 7932, and 7930. We have some confusion amongst people here regarding what the acceptable load for these units are. They are either advertised as 20a or 30a PDUs, but the problem is people seem to think this is the max continuous load these guys can handle. I know otherwise, and know the default 16a Overload is set that way by APC for a reason. I read that you want it to be less the 80% capacity. I just lack the ability to explain why we shouldnt ever go above 16a.

We have some units running at 19amp loads on a 7932. What im looking for is a simple "plain English" explanation as to why this is bad. Or if its not bad, why its not bad, so i can relay the information and clear up confusions.

Thanks!!

Message was edited by: kungfu1

Message was edited by: kungfu1

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

Thanks guys!

Youre always very helpful in answering questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

Thanks for the reply.

So in the case of say, a AP7932, its 30a but is split into 2, 20a circuits from what I understand? So even though its 30a, its still unsafe to run, for example, a 19a load (10amp on bank a, 9amp on bank b) continuously on that unit?

thanks!

Message was edited by: kungfu1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:40 AM

per National Electrical Code, a circuit should not exceed more than 80% of its breaker size.

thus, PDUs and UPSs, etc will have a 15 amp plug and be rated for 12 amps or have a 30 amp plug and only be rated at 24 amps. it is important to note that the breaker would trip at its actual rating - meaning the 15 amp plug would be plugged into a 15 amp breaker and trip when it hits 15 or the 30 amp circuit would actually trip at 30 amps.

[take a look at this article for further info too|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1123]

let us know if you need anything else!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:39 AM

i'll double check tomorrow but you probably mean this has two separate banks on the rPDU. without checking, I am not sure what they are rated at but it should be 80% of whatever the breaker size is on the top of the rPDU.

you should basically distribute the power amongst the banks evenly.

the entire rPDU itself though should not exceed 24 amps, since it has a 30 amp plug on it.

i'll double check tomorrow on what i mentioned here about the banks but i am pretty sure i got that right πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:26 AM . Last Modified: β€Ž2024-03-18 04:39 AM

Great, thanks. Im just a little confused since APC's default setting for Overload is 16a on that unit. I wasnt sure if you shouldnt exceed 16a since theres two 20 amp banks and 80% of 20 is 16. We just had a situation where a PDU died entirely, totally dead and it was under a 19a load, it was a 7932 and im wondering if that load fried the thing over time, or if it was just a bad unit. And again, why the default overload is 16a.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

Gonna reply to myself here as some late-night poking around has yielded the results I was looking for.

I hope others find this useful as well.

Using the AP7932 as an example -

This is a 30a PDU. This model has two banks. Each bank has a 20a breaker, there for you want to balance things evenly between the two banks. If one bank gets overloaded, the breaker will pop, but you only lose half your stuff. Thats a big advantage obviously.

Regardless of the 20a breakers for each bank, this PDU is still a 30a (TOTAL) PDU, but derated to 24a (TOTAL) (30 -80% for electrical code). There for, the overload setting on this PDU should be 24a.

The reason why, in the rPDU web interface/config, even with this model the default setting for overload is 16a, which didnt make sense, is because the rpdu version is model agnostic. It doesnt care what model you have, it just assumes you have a 20a PDU, which 16a overload would be correct for. So if you have a 30a guy, you need to set that to 24a.

Thanks for your replies, feel free to verify what I stated here.

One last question - Does this model (or any model) do staggering by default (power sequencing)? I know the power-on delay can be set through the configs, but ive noticed its set to 0 by default which leads me to believe that by default if the PDU does a cold start, all outlets turn on at the same time and there is no staggering by default. Is this true? If this is true, then to solve that problem id just have to go in and select some/all of the ports and configure them with a power-on delay, correct?

Thanks again and I hope any information i provided here is helpful to others as well.

Message was edited by: kungfu1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

>
One last question - Does this model (or any model) do staggering by default (power sequencing)? I know the power-on delay can be set through the configs, but ive noticed its set to 0 by default which leads me to believe that by default if the PDU does a cold start, all outlets turn on at the same time and there is no staggering by default. Is this true? If this is true, then to solve that problem id just have to go in and select some/all of the ports and configure them with a power-on delay, correct?
Message was edited by: kungfu1>
To answer this question, no by default they will all be set to 0 (or instant power on). The reason being is that we try to make no assumptions about what a customer may need for time delays (as they could potentially vary wildly depending on what a customer is using). As a result, so that we do not create any conflicts from unusably timed staggers, we set them to instantly power on by default. If you wish to, or need to stagger, you would as you mention simply go into the port and configure whatever power-on delay is required by your setup.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

0 Likes
0
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:27 AM . Last Modified: β€Ž2024-03-18 04:39 AM

Thanks guys!

Youre always very helpful in answering questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of