Smart-UPS SUA1500 RMI 2U - AVR Boost

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SUA1500 RMI 2U - AVR Boost
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:19 PM . Last Modified: ‎2024-03-14 04:37 AM

0 Likes
3
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:19 PM . Last Modified: ‎2024-03-14 04:37 AM

Smart-UPS SUA1500 RMI 2U - AVR Boost

Are there some detailed specs about the AVR Boost mode? I like to know for how long an UPS could operate in this mode without any risk of failure.
Thanks a lot

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

0 Likes
1
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

there is no set time. it shouldnt be boosting OR trimming constantly. AVR boost or trim uses an internal transformer to the UPS and creates a lot of heat which will degrade the life of the internal components of the UPS, including the battery, if left on forever (perhaps feeding it lower voltage than the nominal voltage its designed for).

depending on the outside environment and other factors, this UPS could last for 10 years or 4 (purely hypothetical). i am not sure.

if you are constantly boosting or trimming, you need to look into finding out why its happening to avoid killing the UPS prematurely due to extra heat and strain on the UPS components.

hope this helps. let us know if you need anything else.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

0 Likes
0
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

Many thanks for your support and your time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

0 Likes
1
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

there is no set time. it shouldnt be boosting OR trimming constantly. AVR boost or trim uses an internal transformer to the UPS and creates a lot of heat which will degrade the life of the internal components of the UPS, including the battery, if left on forever (perhaps feeding it lower voltage than the nominal voltage its designed for).

depending on the outside environment and other factors, this UPS could last for 10 years or 4 (purely hypothetical). i am not sure.

if you are constantly boosting or trimming, you need to look into finding out why its happening to avoid killing the UPS prematurely due to extra heat and strain on the UPS components.

hope this helps. let us know if you need anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

pipenik
Crewman pipenik
Crewman

Posted: ‎2024-08-16 01:09 PM

In response to BillP
0 Likes
0
943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-16 01:09 PM

Hello, I have APC SmartUPS 1500 model DLA1500I and have problem with turning off the ups when it start regulating AC voltage (AVR Boost mode). When the power consumption at the moment is higher than usual UPS try to regulating low AC voltage, led of AVR Boost start ligthing and UPS after one second immediately turning of and all leds start blinking. What part or relay need change to UPS start working properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore