Smart-UPS SRT 5000 The output power is turned off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 5000 The output power is turned off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
5
2736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

Smart-UPS SRT 5000 The output power is turned off

Hello all!

13 Nov install UPS, 1 week it work and 20 Nov it start turned off by himself. In logs i see:

11/21/2015 04:08:10 Device UPS: Self-Test passed.
 11/21/2015 04:07:49 Device UPS: Self-Test started by management device.
 11/21/2015 04:07:47 Device UPS: The output power is now turned on.
 11/21/2015 04:07:47 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
11/21/2015 03:49:46 Device UPS: The output power is turned off.
 11/21/2015 03:49:46 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn off, sequenced.
 11/21/2015 03:49:46 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced.
 11/21/2015 03:47:11 Device UPS: Self-Test passed.
 11/21/2015 03:46:50 Device UPS: Self-Test started by management device.
 11/21/2015 03:46:49 Device UPS: The output power is now turned on.
 11/21/2015 03:46:49 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 11/21/2015 03:46:49 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 11/21/2015 03:46:48 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn on, sequenced.
 11/21/2015 03:46:48 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn on, sequenced.

Model: Smart-UPS SRT 5000
SKU: SRT5KRMXLI
Serial Number: QS1419272153
Firmware Revision: UPS 02.5 (ID1001)
Manufacture Date: 05/10/2014
 
Apparent Power Rating: 5000 VA
Real Power Rating: 4500 W
 
Battery SKU: APCRBC140

Why is this happening?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

The warranty is direct so APC/Schneider will deal direct to get it swapped, usually an advanced RAM (in the UK)

Unless due to the size they send an engineer but I don't know the policy on big units.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

Hi Pavel,

I'm sorry you are having trouble with this unit. From the logs that you provided it seems like it is being commanded to turn off. I will have to do some more evaluation to determine why. Can you get the support log files off of the unit. You can get these by going to the about->support->generate logs section on the NMC interface. (http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&id=FA156131)

Thanks

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

I have the same problem did you find a fix to this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

I have the same problem did you find a fix to this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

Yep, I'm in the same boat with my SRT-6000 Device that is less than a year old. I thought at first someone was playing games with me and powering off, but it immediately reboots after the forced shutdown. It has happened twice in the last week (at different times).

I'm doing the Tech Support Debug Download now. Now I just have to see where I can send this to.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
2731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:00 AM . Last Modified: ‎2024-02-14 10:34 PM

The warranty is direct so APC/Schneider will deal direct to get it swapped, usually an advanced RAM (in the UK)

Unless due to the size they send an engineer but I don't know the policy on big units.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore