Smart-UPS RT 8000 - Lost setup cd's,cannot configure IP address

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 8000 - Lost setup cd's,cannot configure IP address
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

0 Likes
1
1639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

Smart-UPS RT 8000 - Lost setup cd's,cannot configure IP address

Hi,

Can someone please assist me with a download link for "wizard" setup cd? Ive lost my setup CD's and tried configuring the ups using alternate ways such as the Serial cable hyper terminal method but no luck. I also cant seem to find that MAC address on the NMC card as well....im pretty stuck!!!

Ive already patched the network cable into my switch but cant locate an IP address for this device 😞 Can somebody please assist me?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

0 Likes
0
1639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

You can find the Device IP Config. wizard at the following link:

http://www.apcc.com/tools/download/login.cfm?software_id=DBUE-6EMQCR&sw_sku=SFDIPW301&family=&part_n...

If your browser does not load the page for some reason, the part # for the wizard is SFDIPW301, and searching for it on our web page will bring you to the download section. Keep in mind that this wizard only works for unconfigured network cards. If your device already has an IP the wizard will not be able to configure it.

Have you followed the IP configuration Knowledge Base that we have? I will copy the contents here:

KBASE 3061:


The Network Management Card (AP9617, AP9618, or AP9619) must be configured with network settings >before it can communicate on the network. Once the cards have been configured with an IP address, Subnet >Mask, and Default Gateway the cards can be accessed, managed, and controlled from other computers on >the network.


There are three ways to configure the Network Management Card (NMC) with it's initial settings: the Wizard, >Hyperterminal, and Address Resolution Protocol (ARP).

1. The wizard is included on the CD that comes with the card. The wizard must run on a Windows operating >system. You can configure the card using the wizard over the network via FTP. If using the wizard please >note, the unconfigured NMC must be on the same subnet as the computer running the wizard.


2. Hyperterminal is a built-in function on most Windows operating systems. Before using hyperterminal, any >services using the com ports must be stopped. For example, if you are running a serial version of APC's >PowerChute software, the APC UPS service must be stopped prior to running Hyperterminal. Then, follow >these instructions:

**Please note that if you have the scroll lock on, Hyper-Terminal may not communicate properly with an APC >UPS or
accessory.

Connect UPS to serial port using Smart-signaling cable (940-0024)
Run HyperTerminal
Configure port settings to: 2400 bps, 8 databits, no parity, 1 stopbit, and no flow control.
Save changes.
Press enter to display username prompt.
Use "apc" for username and password.
You are now in the control console.
Choose "Network"
Choose "TCP/IP"
Choose "Boot mode"
Change Boot mode to "Manual"
Set the system IP, subnet mask, and default gateway.
Accept changes.
Press ctrl-C to return to main menu.
Log out of console to save changes.
Now, you can remotely log into the NMC using web access or Telnet.


3. Address resolution protocol (arp) can also be used to configure the NMC. The MAC Address of the NMC >is needed for this method of configuration. The MAC address is located on the quality assurance slip that >shipped with the NMC, and is also located on a white sticker on the NMC itself. From a computer on the >same subnet as the unconfigured NMC, follow these instructions:

Open up a command prompt and type the following (replacing and with actual >values):

Arp-s

**MacAddress format: xx-xx-xx-xx-xx-xx**

On Mac OS X: sudoarp-s

Next, use Ping with a size of 113 bytes to assign the IP address defined by the ARP command.

For the IP address defined in step 1, use one of the following Ping commands:

Windows command format: ping -L113
LINUX and Mac OS X command format: ping -S113

Now, you can Telnet to the card by typing: Telnet
Use "apc" for username and password.
You are now in the control console.
Configure / apply any additional changes.
Log out to save changes.


If you still require additional support regarding the configuration of the Network management Card, please feel >free to call one our technical support representatives at 800-800-4272 (Mon-Fri 8am-8pm EST).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 PM . Last Modified: ‎2024-03-15 12:34 AM

You can find the Device IP Config. wizard at the following link:

http://www.apcc.com/tools/download/login.cfm?software_id=DBUE-6EMQCR&sw_sku=SFDIPW301&family=&part_n...

If your browser does not load the page for some reason, the part # for the wizard is SFDIPW301, and searching for it on our web page will bring you to the download section. Keep in mind that this wizard only works for unconfigured network cards. If your device already has an IP the wizard will not be able to configure it.

Have you followed the IP configuration Knowledge Base that we have? I will copy the contents here:

KBASE 3061:


The Network Management Card (AP9617, AP9618, or AP9619) must be configured with network settings >before it can communicate on the network. Once the cards have been configured with an IP address, Subnet >Mask, and Default Gateway the cards can be accessed, managed, and controlled from other computers on >the network.


There are three ways to configure the Network Management Card (NMC) with it's initial settings: the Wizard, >Hyperterminal, and Address Resolution Protocol (ARP).

1. The wizard is included on the CD that comes with the card. The wizard must run on a Windows operating >system. You can configure the card using the wizard over the network via FTP. If using the wizard please >note, the unconfigured NMC must be on the same subnet as the computer running the wizard.


2. Hyperterminal is a built-in function on most Windows operating systems. Before using hyperterminal, any >services using the com ports must be stopped. For example, if you are running a serial version of APC's >PowerChute software, the APC UPS service must be stopped prior to running Hyperterminal. Then, follow >these instructions:

**Please note that if you have the scroll lock on, Hyper-Terminal may not communicate properly with an APC >UPS or
accessory.

Connect UPS to serial port using Smart-signaling cable (940-0024)
Run HyperTerminal
Configure port settings to: 2400 bps, 8 databits, no parity, 1 stopbit, and no flow control.
Save changes.
Press enter to display username prompt.
Use "apc" for username and password.
You are now in the control console.
Choose "Network"
Choose "TCP/IP"
Choose "Boot mode"
Change Boot mode to "Manual"
Set the system IP, subnet mask, and default gateway.
Accept changes.
Press ctrl-C to return to main menu.
Log out of console to save changes.
Now, you can remotely log into the NMC using web access or Telnet.


3. Address resolution protocol (arp) can also be used to configure the NMC. The MAC Address of the NMC >is needed for this method of configuration. The MAC address is located on the quality assurance slip that >shipped with the NMC, and is also located on a white sticker on the NMC itself. From a computer on the >same subnet as the unconfigured NMC, follow these instructions:

Open up a command prompt and type the following (replacing and with actual >values):

Arp-s

**MacAddress format: xx-xx-xx-xx-xx-xx**

On Mac OS X: sudoarp-s

Next, use Ping with a size of 113 bytes to assign the IP address defined by the ARP command.

For the IP address defined in step 1, use one of the following Ping commands:

Windows command format: ping -L113
LINUX and Mac OS X command format: ping -S113

Now, you can Telnet to the card by typing: Telnet
Use "apc" for username and password.
You are now in the control console.
Configure / apply any additional changes.
Log out to save changes.


If you still require additional support regarding the configuration of the Network management Card, please feel >free to call one our technical support representatives at 800-800-4272 (Mon-Fri 8am-8pm EST).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore