Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS RT 5000VA XLI 230VAC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000VA XLI 230VAC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
4
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

Smart-UPS RT 5000VA XLI 230VAC

Hello,

I have stored an working APC Smart-UPS RT 5000VA XLI 230VAC for 9 months, and now want to get it back working.

And I'm now getting A/D Converter Fault, the RED X flashes, and 3 battery LEDs are ON.

In the webpage I've got a reading of more than 455VAC, with the 230VAC powered or not...

The batteries are 2 years old, I think they need to be replaced, but I've never got this kind of error (A/D FAULT).

If I place a new batteries it should work? I do not want to spend some money and then trash the unit...

Is there a way to test the unit without new batteries?

I've got this warnings:

Critical Events - UPS: A battery bus soft start fault exists.

Critical Events - UPS: An analog-to-digital (A/D) converter fault exists.

Critical Events - UPS: Bypass not in range ; high voltage.

Critical Events - UPS: The output power is turned off.

Informational Events - UPS: A DC bus overvoltage no longer exists.

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

Hi Julio,

 

I am sorry to hear that. It does seems that the fault resides with the unit at this point. We do offer a trade-ups program where you can get a 15-25% discount on a new unit. Please let me know if you have any other questions that I can help you out with.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

Hi Julio,

I believe that your issue would be batteries. Storing the unit for 9 months will cause the batteries to go bad. The unit will not turn on with bad batteries. Many times bad batteries are the cause of the faults you are seeing. One thing you can do to see if the batteries are indeed bad is to test the voltage we are getting from the battery modules. You would measure the DC voltage at the anderson connector for each unit. Each module will measure about 110 volts when fully charged. If they are below roughly 85 volts the batteries would be considered unrecoverable and dead. Now if the batteries do come back as bad I would recommend replacing them but there is still a chance that these faults lie with the unit. 

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

Dear Mike,

Thanks for your answer.

I have charged the batteries with a DC power supply, and I do not think they are good, even they measure 12,7V.

When charged I've raised the voltage to 16V and they charge at 0,3A, at this voltage it's supposed to drain more than 1A...

They start at 1A but in less than 1 minute it drops to 0,3A or less, and I can hear bubbling inside...

While one or two still keep 13,5V with 1A.

So the batteries are no good for sure.

My only issue is if the unit it's good if I change the batteries...

I'm afraid of spending money on new batteries to trash the unit and new batteries...

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

I have changed the batteries and I have the same problem...

The UPS starts with 3 battery leds and X red led lit.

Then after 5 seconds it seams to restart, and I hear some relays switching...

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:58 PM . Last Modified: ‎2024-03-06 03:26 AM

Hi Julio,

 

I am sorry to hear that. It does seems that the fault resides with the unit at this point. We do offer a trade-ups program where you can get a 15-25% discount on a new unit. Please let me know if you have any other questions that I can help you out with.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore