Smart-UPS RT 5000 XL - Discharged Battery (Critical) Efter a New Battary Replaced

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 XL - Discharged Battery (Critical) Efter a New Battary Replaced
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:52 AM

0 Likes
4
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:52 AM

Smart-UPS RT 5000 XL - Discharged Battery (Critical) Efter a New Battary Replaced

Hi,

I'm trying to figure out what to do next, we did a recent battery change the 2017 11/23th and it all looked fine. Then after a first Self-test it started to have a LED Blink for issues. The logs show a critical warning:

Discharged Battery

What would be the next step to check or to change so to resolve the issue?

I noticed the very low runtime remaining and also that the batteries are fully 100% charged.

UPS

Firmware Revision: 5.1 (ID5)
Manufacture Date: 05/05/2013

No external Batteries! Only Internal batteries.

The Event Log

11/23/2017 06:21:47 UPS: A low battery condition no longer exists.
11/23/2017 06:21:47 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/23/2017 06:21:46 UPS: passed via internal operation a self-test.
11/23/2017 06:21:39 UPS: A discharged battery condition no longer exists.
11/23/2017 06:21:39 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/23/2017 06:21:38 UPS: Started a self-test.

rxuN2Q3TZ%2BJcQAM6l5Dy9g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngrxuN2Q3TZ%2BJcQAM6l5Dy9g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

My apologies Poul, I did miss that.

In addition to what Mark said, if these are recent APC batteries and runtime calibration doesn't increase the estimated runtime, I would call APC to get it sorted out.

If runtime calibration won't complete because the UPS thinks the batteries are bad, you can unplug the UPS to force it to run as long as it can. Make sure you have no critical loads on the UPS and that you have at least 30% load so that runtime parameters can be estimated.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:52 AM

0 Likes
0
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:52 AM

Hi Poul,

If your batteries are as old as the UPS (4 years), they may be due for replacement. Typical lifespan for lead acid batteries is 3-5 years. As batteries age, their capacity decreases so 100% charged is less and less charge. And the less charge the battery holds, the less runtime they provide.

During the battery self-test, the UPS updated its runtime estimate based on the observed condition of the battery.

"Discharged Battery" warns you when the estimated runtime drops below the "low battery duration" which is generally the amount of time needed to safely shut down attached loads.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:51 AM

Hi voidstar,

Thanks for your reply. If you noticed in my post I was trying to clearly point out that this issue persist with freshly new changed batteries. Thus my perplextion. If you have any other advice please assist.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:06 AM . Last Modified: ‎2024-03-18 12:51 AM

Did you run the battery calibration routine?  If you use more than 30% of the rated load and take the batteries to alarm state by disconnecting the mains, they will usually recalibrate fine - without having to totally discharge them as the "calibration" test does, (which is damaging to some extent).  I'd try that first and record how long it takes to actually discharge - and compare to the technical charts of "run times".  If the run time is actually very short you might have new battery issues!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

My apologies Poul, I did miss that.

In addition to what Mark said, if these are recent APC batteries and runtime calibration doesn't increase the estimated runtime, I would call APC to get it sorted out.

If runtime calibration won't complete because the UPS thinks the batteries are bad, you can unplug the UPS to force it to run as long as it can. Make sure you have no critical loads on the UPS and that you have at least 30% load so that runtime parameters can be estimated.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of