Smart-UPS RT 5000 User authentication problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 User authentication problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
9
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

Smart-UPS RT 5000 User authentication problem

Hi

I have to reconfigure a number of these UPS's and although I reset them to the default apc username and password I seem to be unable to log on with the new credentials I supply for the administrator. At the moment I am unable to sign in via the console, web or ssh.

How do I create a username and password for all three these access types?

Thanks

Karl

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

Ok. Its working now, but only after I reset the network management module to factory defaults. Thanks for the assistance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

Hi Karl,

I'll need to know what UPS Network Management Card model you're using in that UPS - it should say it on the rear of the UPS. I suspect either AP9619 or AP9631. If AP9631, I need to know what firmware which when you access it via web, is it a blue/white screen or green and white and that will tell me.

I also want to double check to make sure I understand the question. Do you need to reset the user name and password to gain access? Or are you looking to understand how to mass configure devices with a new user name and password?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

Hi Angela

Thanks for the quick response. I inherited a number of these UPS's and as usual nothing was documented. As such I need to reset the admin password and essentially be able to gain ssh, web and console access. The web screen is blue and white and model number of that card is: AP9619

Thanks

Karl

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

I managed to find the user manual for the AP9619 at: http://www.apcmedia.com/salestools/PMAR-8KRDZG/PMAR-8KRDZG_R0_EN.pdf

but I followed the procedure to reset the administrator password and I am still unable to get in with the changed credentials.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

Let's start at the beginning. You're getting the user name and password prompt via serial connection, correct? So you know your terminal session is set up properly. Then what you should be doing is pressing the pinhole reset button once and in response to that, the status LED (the one with the checkmark or X next to it) will almost immediately begin flashing rapidly green and orange (amber). Right when that happens, you need to press the status LED a second time and the status LED should go off. As soon as that happens, you need to go back to the terminal session you had and press enter once every several seconds until the username prompt comes back. You have a 30 second window here to log in with apc/apc temporarily before it resets back to the unknown credentials. Then, you need to go into the System->User Manager Menu and reset the administrator username and password to something you know or else when you log out of the session or it times out from inactivity, it will go back to the unknown credentials.

Can you let me know how far you made it and what you saw? I suspect either a step was missed or performed incorrectly or the reset button is missing, physically damaged, or was not pressed if the object you used was too large or mis-aligned.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

I have done exactly what you said above. Pressed rest twice and managed to log in with apc/apc. Then went to User manager and changed the administrator username and password. Committed the changes and logged out (serial connection). immediately after that I am unable to connect using the new admin username and password. To test that the changes have taken effect I immediately do the reset thing again and log on with apc/apc for the second time. I then go to user manager and can see that the admin username has indeed changed. So, at this stage i'm starting to think something is faulty, since it clearly registered that I reset the username and password. I don't know what to do next and I really need to be able to monitor these ups's via snmp soon!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

well, another option is if you're able to get in with apc/apc, then you could go to System->Tools and Reset to Defaults and wipe the entire card if you're OK to wipe all existing settings.

The only thing I can see as an issue would be something like CAPS lock or Num lock causing a problem with the password your setting. I don't think anything is "faulty" based on my experience rather than the perception it isn't working because of CAPS lock, Num Lock, or even something going on with special characters where it is not accepting those but not clearly telling you. Are you using special characters? And perhaps you've already ruled out CAPS lock or Num lock being an issue..

Can you try to set the username and password back to just apc/apc for testing after it lets you in with that after saving?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

Ok. Let me try that. If apc/apc does not work i'll wipe the card by going to defaults.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

You're welcome. smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

0 Likes
0
2345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:23 AM

Ok. Its working now, but only after I reset the network management module to factory defaults. Thanks for the assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore