SmartUPS SMX3000RMHV2U. Switch On Server when Power restoring

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS SMX3000RMHV2U. Switch On Server when Power restoring
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
6
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

SmartUPS SMX3000RMHV2U. Switch On Server when Power restoring

Hi Everybody!

We have recently added a smart UPS mod. SMX3000RMHV2U to our rack together with an HP Proliant ML350G6 server.

LastFriday,the power-networkhas fallenand the UPSsuccessfullysupportedthe equipmentfor about3hoursthenproceededtoturn off the server.

Then for about48hoursthe serverhas beenturned off!

What i would like to know is if there's a way to send a command (or a specific configuration) to switch on the server (if it has been switched off by the UPS) after power-network is restored.

ps:

before install this Smart UPS we used for a long time another small SmartUPS up to 1500VA but now we need more power.

After the substitution, the upgraded version of powerchute (9.1 build 615) doesn't recognize the server anymore.

Trying to establish a connection Powerchute report he can't find the agent ("unknow device") however with "WEB Agent interface" we can make the connection and configure the UPS.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

I think i have the right settings (see attached collage).

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

Hi Everybody!

We have recently added a smart UPS mod. SMX3000RMHV2U to our rack together with an HP Proliant ML350G6 server.

LastFriday,the power-networkhas fallenand the UPSsuccessfullysupportedthe equipmentfor about3hoursthenproceededtoturn off the server.

Then for about48hoursthe serverhas beenturned off!

What i would like to know is if there's a way to send a command (or a specific configuration) to switch on the server (if it has been switched off by the UPS) after power-network is restored.

ps:

before install this Smart UPS we used for a long time another small SmartUPS up to 1500VA but now we need more power.

After the substitution, the upgraded version of powerchute (9.1 build 615) doesn't recognize the server anymore.

Trying to establish a connection Powerchute report he can't find the agent ("unknow device") however with "WEB Agent interface" we can make the connection and configure the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:43 AM . Last Modified: ‎2024-03-05 12:24 AM

Dear Angela,
thank you for your prompt reply.

I assuming server has the right config on Bios (tomorrow i will check it) but in the meanwhile i check the UPS config and found, i suppose, a wrong parameters (see attached file).

IfI interpretcorrectlythat parametermeans, when battery isexhausted, UPSremainsturned off (theneitherthe server will not berestarted).

Can you confirm it?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

Hello again!

No, that setting does not impact what I said. As soon as the "low battery" condition is true, the UPS will start a shut down, and wait for AC power to return. The low battery setting is also able to be adjusted by the user. By default, it is at 2 minutes meaning when the UPS runs on battery and only has 2 minutes of runtime remaining, it will say low battery! and force the PowerChute Business Edition Agent to start a shutdown. The user can increase that value if they want, for example, if their device/server takes longer than 2 minutes to shutdown. Either way, the UPS should turn back on when AC power returns.

Can you check the event log to see if the scenario you mentioned if the UPS turned back on? We'll need to know that. Or, when you noticed your server was off, did you have to turn the UPS back on or just the server?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

"Can you check the event log to see if the scenario you mentioned if the UPS turned back on?"

See attached file.

".. when you noticed your server was off, did you have to turn the UPS back on or just the server?"

Yes i turned On the UPS too. (Sunday, 4th May 12:01)

(Note: Therewasa bigstormonMay3 at 6PM and we hearda biglightningfall to the groundin the quarters)

Attachments
EventLog.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

Hi,

Check the settings in PowerChute to be sure the UPS has been configured to power the outlets back up when AC returns. There are 2 settings. The first is under Outlet Sequence and the second is under Load Shedding.

2352_pastedImage_0.png

2353_pastedImage_1.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

0 Likes
0
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:44 AM . Last Modified: ‎2024-03-05 12:24 AM

I think i have the right settings (see attached collage).

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of