Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Smart-UPS Causes Power Loss to Connected Devices

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS Causes Power Loss to Connected Devices
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
AndyDixon_apc
Crewman AndyDixon_apc
Crewman

Posted: ‎2021-06-30 08:58 PM

0 Likes
6
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:58 PM

Smart-UPS Causes Power Loss to Connected Devices

This was originally posted on APC forums on 10/23/2016


Hello, I'm hoping someone can help me with an issue I've encountered with one of our SURTD3000XLI models. The UPS unexpectedly rebooted the other day, causing the 10 Cisco 2960 access switches connected to it to reboot. My understanding is that these online models should 'fail on', thanks to their automatic internal bypass feature, meaning that the access switches should not have rebooted.

My initial question is therefore, is my understanding of my model's expected behaviour correct?

I should add that the UPS was in online mode at the time of its unexpected reboot (i.e. the manual bypass switch at the back of the unit was in the 'Online' position).

I'd be grateful if anyone could share their expertise of this UPS model with me. Whilst I have now replaced the suspected faulty 3000XLI unit with a 3000RMXLI unit, I have a number of other 3000XLI models out there, supporting our networking estate. I therefore urgently need to understand more about the expected behaviour of them during UPS fault scenarios.

Thanks in advance.

Andy

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • automatic
  • bypass
  • feature
  • reboot
  • surtd3000xli
  • Unexpected
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Kiriakos_GR_apc
Ensign Kiriakos_GR_apc
Ensign

Posted: ‎2021-06-30 08:59 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:59 PM

This was originally posted on APC forums on 10/31/2016


Faulty electrical relays are the ones not responding at expected milliseconds of time.

Under such issues UPS become slow to respond, and anything connected will suffer from power loss.

See Answer In Context

Reply
Share
Replies 6
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:58 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:58 PM

This was originally posted on APC forums on 10/23/2016


The UPSes are supposed to go to bypass during a fault providing the input voltage is within the acceptable bypass limits. If there is a problem with the bypass system, then a subsequent UPS fault could drop the load.

Big picture, we buy UPSes to prevent downtime, but UPSes themselves can fail causing downtime. This trade-off is a win if you have frequent power failures, but suppose you're aiming for even greater reliability... what to do? There are a few options:

1) The Symmetra line of UPSes has redundant power modules so both the redundant modules and the bypass system would have to fail. Although this is much more reliable there are still ways this could fail, so...

2) Often critical equipment is dual-corded having redundant power supplies. So you put a separate UPS on each supply. The nice thing about this arrangement is both power paths are active, so you're more likely to detect failures before they become a problem. It looks like Cisco 2960 switches can have redundant supplies.

3) Sometimes even that isn't enough, so instead of spending money keeping a piece of infrastructure up, you can allow it to go down and automatically failover to redundant infrastructure.

Reply
Share
AndyDixon_apc
Crewman AndyDixon_apc
Crewman

Posted: ‎2021-06-30 08:58 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:58 PM

This was originally posted on APC forums on 10/23/2016


Hi Voidstar. Thanks very much for taking the time to respond. Really appreciate it.

Do you think its worth checking the bypass limits of my other UPSes, in case the current thresholds in play would prevent a bypass during a fault? (I'm assuming this check, and any subsequent adjustments, can be done via the serial interface, or remotely via our StruxureWare software).

I also intend to remotely reboot of the UPSes out of hours, to see whether the process causes the access switches to reboot. Everything I read about the UPS model involved suggests that a reboot Should NOT affect connected devices, but I'd still like to see it for myself.

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:59 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:59 PM

This was originally posted on APC forums on 10/23/2016


You can certainly check the bypass limits. Note that the UPS will throw an alarm "Bypass out of range" when the input is outside the bypass limits so presumably StruxureWare would already be telling you when this is the case.

I'm not entirely clear what you mean by "reboot". If you mean reboot the network management card (NMC), then yes, the UPS is unaffected -- the NMC is it's own separate processor. On the other hand, you can also reboot the UPS output under control->ups or control->outlet groups. Unless the load has redundant power supplies or it's own backup battery, it will be affected.

Reply
Share
AndyDixon_apc
Crewman AndyDixon_apc
Crewman

Posted: ‎2021-06-30 08:59 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:59 PM

This was originally posted on APC forums on 10/23/2016


Well, we didn't see anything in our StruxureWare logs, so its likely that the thresholds set are okay.

I did mean a reboot of the device. One of our network engineers was adamant that power to connected devices is not affected by a reboot, whereas previous experience of colleagues suggests otherwise. Its likely that the network engineer is basing his opinion on another UPS model (perhaps one with redundant power supplies).

 

Anyway, I think I have enough to go on so, thanks once again for your input.

 

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:59 PM

0 Likes
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:59 PM

This was originally posted on APC forums on 10/23/2016


Some devices have enough energy storage to survive a short loss of power. Maybe the network engineer is familiar with a switch like that? It's a bit of a problem if you want the device to actually reboot, so the UPS has a "reboot delay" setting that can be increased if necessary to ensure the device turns off before turning it back on.

Reply
Share
Kiriakos_GR_apc
Ensign Kiriakos_GR_apc
Ensign

Posted: ‎2021-06-30 08:59 PM

0 Likes
0
301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:59 PM

This was originally posted on APC forums on 10/31/2016


Faulty electrical relays are the ones not responding at expected milliseconds of time.

Under such issues UPS become slow to respond, and anything connected will suffer from power loss.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc