Smart UPS-Battery near end of life error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS-Battery near end of life error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

0 Likes
5
46260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

Smart UPS-Battery near end of life error

I have looked around and can't find any data on this type of error:

We just finished upgrading 190 APC 1500 and 2200 UPSs.  The equipment is all manufactured in 2018 running version 6.5.0 on the NMC. Besides finding 5 units that were DOA, the equipment is all up and working. I now have 6 out of the 190 units showing an alarm of "Battery near end of life". The battery install date on the UPS indicates February or March of 2019. I ‘ve tried resetting the battery health warning to 730 days and back to no response. Setting the time to no response clears the alarm but as soon as I set it back to default values it goes back into a warning alarm. This is an SNMP alarm that shows up in DCE and in the UPS log. I am not able to find this problem on any of the past community questions.

Any help would be most appreciated. 

Chuck

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • error
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

0 Likes
2
46216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

It looks like resetting the "battery health alarm warning time" to -1 (no notification warning) and back to default of 183 days cleared the alarm. The function is located under the UPS configure tab of the NMC. This action worked on all of the problem UPSs. I am not sure why the alarm triggered with a new UPS install but it's now all green status. 

Chuck

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

0 Likes
0
46216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

Hi Chuck,

Is the alert active only on the SNMP web interface and DCE, or does the UPS LCD display also indicate active alert? Which UPS series are you using, could you let me know the model number of one of your 1500VA and 2200VA units?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

0 Likes
0
46216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

The error shows up on both the event logs and on the front of the display of the equipment. It shows up on both the SMT2200RM2UC and SMT1500RM2UC units. It has only showed up on a few units out of the 190 units we installed. 

Chuck. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

0 Likes
2
46217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 AM . Last Modified: ‎2024-03-15 05:58 AM

It looks like resetting the "battery health alarm warning time" to -1 (no notification warning) and back to default of 183 days cleared the alarm. The function is located under the UPS configure tab of the NMC. This action worked on all of the problem UPSs. I am not sure why the alarm triggered with a new UPS install but it's now all green status. 

Chuck

Reply

Link copied. Please paste this link to share this article on your social media post.

LEDEng
LEDEng
Cadet

Posted: ‎2023-10-25 04:14 AM . Last Modified: ‎2023-10-25 06:26 AM

In response to BillP
0 Likes
1
28878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-25 04:14 AM . Last Modified: ‎2023-10-25 06:26 AM

Hi I have the same problem with one of our SRT2200 units, But I can't find the "Battery Health alarm warning time" in the config menu. The settings I see are "Replace battery notification" (183days) and "replace battery alarm reminder"(14days). I cannot set either of these to -1. Am I missing something?

 

Update: I have fixed the problem by setting the battery fitted time to todays date, then setting it back to the original instal date.😊

 

Reply

Link copied. Please paste this link to share this article on your social media post.

dimitrisb
Crewman dimitrisb
Crewman

Posted: ‎2025-05-20 01:37 AM

In response to LEDEng
0 Likes
0
110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-20 01:37 AM

Hi

How did you reset the battery fitted date?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of