Smart UPS AVR Trim and Boost Calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS AVR Trim and Boost Calibration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

0 Likes
8
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

Smart UPS AVR Trim and Boost Calibration

Hello,

I need to know the steps to configure my APC Smart UPS 1500 correctly via serial cable. The repair guy corrected battery problem of low backup and said that Trim is not a problem, however, since he left I am noticing the UPS AVR trim continuously even when the line voltage is near perfect i.e. 230 VAC. The UPS transfers to battery power when the line voltage is around 235 VAC.

I am not sure if this is a real problem or not but I am very sure that this is not normal.

Please help.

Thank you.

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1500
  • avr
  • boost
  • serial
  • smart
  • trim
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:50 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:50 PM . Last Modified: ‎2024-03-06 10:36 PM

Hello Bill,

I did the Braindead procedure. The UPS wasn't starting up, so i had to cold start it. Next, I logged in via serial and checked the model, nothing was different. Had to increase UpperLineVoltage to 114 and it switched to utility power, however, the trim is still present.

I called the local support. Let's see how they respond.

 

Thank you for your valuable time and support.

kind regards,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

Hi Obaid,

Do you have the model number for your ups. It should be on a white sticker on the back. This will allow me to better assist you. 

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:37 PM

Yes, the model number is: SUA1500I.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

Hi,

If you install PowerChute Business Edition Agent or APCUPSD and connect to the UPS using the serial cable you can adjust the transfer points. You can also adjust the transfer point using a terminal program and using information found in the UPS-Link you can adjust the transfer point. Information on UPS-Link protocol can be found in Kbase FA276164

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

Hello Bill,

Thank you for the detailed information. It is helpful.

The model detected during the installation of Powerchute Business Edition Agent is: "Smart-UPS ???2 RM XL ??"
Do you think there is a problem with this model number number?

Adding more info: The UPS is connected to 230 VAC, while in APCUPSD it is showing Line Voltage: 120.9 V, HighTrans: 108 V, LowTrans: 92 V, OutPutV: 101 V.

According to my knowledge, RM is shortcode for Rack Mount, which this UPS is not. The voltage info from UPS is also not accurate.

File is Attached for reference.

Please share your opinion and fixes.

Thank you,

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

Hi,

That is not normal behavior. Was this UPS purchased new or used and from an authorized APC / Schneider Electric partner? If the unit was recently purchase new from a APC / Schneider Electric partner you should contact local APC / Schneider Electric technical support for a replacement. If the unit was purchased used you should contact the sell for a replacement.

I cannot be sure without having the unit but the software indicates the unit has been tampered with. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

I purchased it locally almost a year ago and they claim to be authorized resellers / partners.

When they visited recently, UPS was reporting similar "???? ?????????" in name and they fixed it through hyperterminal. They told us that frequent power failures erase or interfere with UPS memory. I do not know if the unit is tampered and the possibility is least because there is no such professional tech hacker in this country.

There must be a solution for such a problem or steps to get original OEM software or firmware.

Awaiting positive response.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:49 PM . Last Modified: ‎2024-03-06 10:36 PM

Hi,

Unfortunately there is no way to upgrade the firmware on a SUA model Smart-UPS. There is a way using hyperterminal to set the name however the UPS is reporting an incorrect serial number and voltages. The serial number is hard coded and the unit is reading the incoming voltage incorrectly. You should try to reset the unit (see Kbase FA156611). If that does not resolve the issue since the unit is only a year old it should still under manufacture warranty so you should contact local support for assistance.

You can find the local support contact information at this link. http://www.apc.com/site/support/index.cfm/contact-information/ 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:50 PM . Last Modified: ‎2024-03-06 10:36 PM

0 Likes
0
5579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:50 PM . Last Modified: ‎2024-03-06 10:36 PM

Hello Bill,

I did the Braindead procedure. The UPS wasn't starting up, so i had to cold start it. Next, I logged in via serial and checked the model, nothing was different. Had to increase UpperLineVoltage to 114 and it switched to utility power, however, the trim is still present.

I called the local support. Let's see how they respond.

 

Thank you for your valuable time and support.

kind regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore