Smart UPS 5000 - Discharged Battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 5000 - Discharged Battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
5
2939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

Smart UPS 5000 - Discharged Battery

We have just installed a brand new Smart UPS 5000 into our server rack. The load on it is pretty high (see numbers below):

Load in Watts - 80%
Battery Capacity - 100%
Runtime Remaining - 2 Minutes

However this UPS will continually alternate from no Critical Errors, to a Discharged Battery Error. It will do this every few seconds, alternating between no errors, to error.

I understand that the load is high. When I shut down some servers, the stability improves.

However in the next rack over, we have an indentical UPS, with pretty much the same numbers. It never generates that error message. Runtime remains stable, etc.

I checked the firmware on them, and both are running the same version.

Any help would be appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

On the Faulty UPS

Load in Watts - 73.3%
Battery Capacity - 100%
Input Voltage - 201.5 VAC
Output Voltage - 201.5 VAC
Runtime Remaining - 2 Minutes
Low Battery Threshold - 2 Minutes

It appears that the UPS is mis-reading its Runtime. The other UPS (the 5000 that is working) has a higher load (85%) but after its latest runtime, is showing 7 minutes remaining.

NOTE: Contacted Dell, who is going to ship us another UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

Adam,

Check this document which addresses this issue. You will experience this situation whenever the UPS runtime is less than 2 minutes when the unit is operating online. If possible, could you please post some of the logs which are being recorded by the Power Chute? Could you please check the other Identical UPS runtime and its load power draw?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

We are currently not running PowerChute, so I don't have any logs at present. I will get it installed however, and see if that helps.

On the UPS that is causing the issues, here is what we will see in its log file:

11/07/2009 10:12:20 UPS: A low battery condition no longer exists.
11/07/2009 10:12:20 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/07/2009 10:10:48 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/07/2009 10:10:48 UPS: A discharged battery condition no longer exists.
11/05/2009 06:08:33 UPS: A low battery condition no longer exists.
11/05/2009 06:08:33 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/05/2009 06:08:25 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/05/2009 06:08:25 UPS: A discharged battery condition no longer exists.
11/04/2009 06:50:24 UPS: A low battery condition no longer exists.
11/04/2009 06:50:24 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/04/2009 06:50:22 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/04/2009 06:50:22 UPS: A discharged battery condition no longer exists.
11/04/2009 06:29:52 UPS: A low battery condition no longer exists.
11/04/2009 06:29:52 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/04/2009 06:29:48 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/04/2009 06:29:48 UPS: A discharged battery condition no longer exists.

This condition will clear, and then appear again, clear and appear, etc.

I just ran a run-time config, and am getting a run-time remaining of 0 minutes (it was at 2 before I ran the run-time). Power and load numbers on the problem UPS:

Load in Watts - 73.3%
Battery Capacity - 36% (Due to run-time test).
Input Voltage - 204.1
Output Voltage - 204.1
Runtime Remaining - 0 Minutes

On the other UPS (Identical Model) I am getting the following:

Load in Watts - 85.2%
Battery Capacity - 100%
Input Voltage - 204.1
Output Voltage 204.1
Run-Time remaining - 9 Minutes.

So it really doesn't makes sense. The flaky UPS has less load on it, but is reporting the wrong numbers. At this point I am not sure what we should do. I am thinking of checking the battery connections...maybe one is loose?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

An update to my last post.

Both UPS Devices have restored 100% battery power, from the Run-Time config. However the flaky UPS is still showing under 2 minutes of run-time, while the stable one (with the higher load) is showing 7 minutes.

Does that sound like we have a bad battery? What other steps should I take?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

Adam,

Now that you've run a runtime calibration can you post the latest data that you have on your computer?

Please tell us what you currently have for the following:
*Load in Watts
*Battery Capacity
*Input Voltage
*Output Voltage
*Runtime Remaining
*Low Battery Threshold / Signaling Time

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

On the Faulty UPS

Load in Watts - 73.3%
Battery Capacity - 100%
Input Voltage - 201.5 VAC
Output Voltage - 201.5 VAC
Runtime Remaining - 2 Minutes
Low Battery Threshold - 2 Minutes

It appears that the UPS is mis-reading its Runtime. The other UPS (the 5000 that is working) has a higher load (85%) but after its latest runtime, is showing 7 minutes remaining.

NOTE: Contacted Dell, who is going to ship us another UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of