Smart-UPS 1400 giving "Batteries Discharged" with New batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1400 giving "Batteries Discharged" with New batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
HDRW_apc
Crewman HDRW_apc
Crewman

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
6
3577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

Smart-UPS 1400 giving "Batteries Discharged" with New batteries

I have a Smart-UPS 1400 (among others!) which was reporting "Batteries Discharged" for some time, although the status was showing 100% charge level, and 27.74 Volts.
I changed the batteries for a new set, and it's still the same!
It flips in and out of "Discharged", sometimes spending a minute or two in the "Discharged" state, sometimes only a few seconds - here's a section of the reports that it emails:
***
Date: 10/29/2009
Time: 11:32:34
Code: 0x0108

Informational - UPS: Battery discharge condition cleared.
***
Date: 10/29/2009
Time: 11:32:35
Code: 0x0107

Severe - UPS: Batteries discharged.
***
Date: 10/29/2009
Time: 11:36:14
Code: 0x0108

Informational - UPS: Battery discharge condition cleared.
***
Date: 10/29/2009
Time: 11:36:15
Code: 0x0107

Severe - UPS: Batteries discharged.
***
I tried to do a Run-Time Calibration, but it immediately reported "Low Battery" and stopped the calibration, showing a 3% charge level, despite the voltage still reading 27.74!

So:
1) If it's not using the voltage to decide if the batteries are discharged, what is it using?
2) What can I do about this? How can I get it working properly again?

Cheers, Howard

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • discharged
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

try this technique http://www.IngenuityRedefined.com/APC

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
HDRW_apc
Crewman HDRW_apc
Crewman

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

I have a Smart-UPS 1400 (among others!) which was reporting "Batteries Discharged" for some time, although the status was showing 100% charge level, and 27.74 Volts.
I changed the batteries for a new set, and it's still the same!
It flips in and out of "Discharged", sometimes spending a minute or two in the "Discharged" state, sometimes only a few seconds - here's a section of the reports that it emails:
***
Date: 10/29/2009
Time: 11:32:34
Code: 0x0108

Informational - UPS: Battery discharge condition cleared.
***
Date: 10/29/2009
Time: 11:32:35
Code: 0x0107

Severe - UPS: Batteries discharged.
***
Date: 10/29/2009
Time: 11:36:14
Code: 0x0108

Informational - UPS: Battery discharge condition cleared.
***
Date: 10/29/2009
Time: 11:36:15
Code: 0x0107

Severe - UPS: Batteries discharged.
***
I tried to do a Run-Time Calibration, but it immediately reported "Low Battery" and stopped the calibration, showing a 3% charge level, despite the voltage still reading 27.74!

So:
1) If it's not using the voltage to decide if the batteries are discharged, what is it using?
2) What can I do about this? How can I get it working properly again?

Cheers, Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:05 PM . Last Modified: ‎2024-03-14 03:45 AM

The battery constants give the battery status via their life expectancy. If the battery ages and is “exhausted”, the constant is overwritten. The management software calculates the runtime of the UPS with these constants.If the battery is now replaced, a self test must be done with the new batteries. Through it, the red battery replace indicator goes out and the battery constants should be reset to the standard settings. This does not occur in some cases. Therefore, the constants must be reset manually in order to correct this situation. Please call in the regional APC Customer Care Center as they can walk you through the steps to adjust the battery constant manually.

Reply

Link copied. Please paste this link to share this article on your social media post.

HDRW_apc
Crewman HDRW_apc
Crewman

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

Thanks, a very helpful tech support person gave me the information on how to re-set the figure, which was1E, to 9A, and it's all now working properly.
There was a bit of a glitch in determining what the correct figure should be, because it's a very old device, but we got there in the end!

Cheers, Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

I have the same problem with an old SUA2200XL with brand enw batteries. it worked great, I self-tested with the new batteries, showed a 500minute run time, then I restored the load and logged into the console and I find that I have 7% battery left and I ran self-test, but would not let me.

How do I change that constant parameter manually?

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

Hello Michael,

Have you tried running a runtime calibration from the software that you are using? Aside from that battery percentage are you also seeing flashing LED's on the UPS? If you do can you tell us what are those LEDs? Below is an APC KnowledgeBase Article which I hope could help you out, if not please call the APC Customer Care Center and they would be able to help you out should there be a need to change the constant.

[Why are the battery charge LEDs flashing on a Smart-UPS?|http://nam-en.apc.com/app/answers/detail/a_id/1497/kw/flashing%20BBG]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

0 Likes
0
3567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:06 PM . Last Modified: ‎2024-03-14 03:45 AM

try this technique http://www.IngenuityRedefined.com/APC

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of