Smart UPS 3000xl and electric generator.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 3000xl and electric generator.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
5
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

Smart UPS 3000xl and electric generator.

Hi, we have two problems with a Smart UPS 3000 XL
1) The UPS continues to transfer online to battery power when powered by our HONDA EG 6500 CXS (5KVA) electric generator.

2) We do not have the cable to connect the UPS and be able to configure it, to adjust the voltage distortion (possible cause of the problem).
Anyway, we need the cable or the pin out scheme to make the cable.

From now on I am very grateful for any help or suggestion.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

On 15/12/2020 8:59 PM, Damian said:

First of all, I apologize for the delay in my response.

Your help solved my problems.

Brilliant. Thanks for coming back to say so. Many people don't come back with a "that worked", so this makes it useful for others in the future. Glad I could help.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

Which SmartUPS 3000XL? There are several generations now. What's the actual tag on the UPS say? What connector does it use? If it's a D9 there are plenty of places on the net you can find the cable pinout (the APCUPSD manual is one a quick search will turn up).

Unless your Honda is an inverter gen, you might struggle. The UPS will look at both the voltage and (more importantly) frequency variation and if it moves around much it'll just keep transferring to battery. Some of the older gen of UPS had a button and LED on the back you could use to change the sensitivity settings also.

I recall a few years ago now running an SU2200 on a standard gen but I recall having to keep a very stable load to allow the UPS to charge the batteries. I switched to a cheap inverter gen and haven't had an issue since.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

Thanks you Brad

Your help was really helpful.

The UPS model is Smart 3000XLI.

As you said, it has the led and the button to adjust the sensitivity. ( https://imgur.com/RYoBQPi )

I looked in the documentation ( https://www.apc.com/shop/fi/en/products/APC-Smart-UPS-XL-3000VA-230V-Tower-Rack-Convertible/P-SUA300... ).


but I didn't see anything on how to use the led and sensitivity button.

And the same for the cable or pinout of the DB9

Could you help me with these things?

Thanks a lot!

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

On 9/12/2020 10:37 PM, Damian said:

I didn't see anything on how to use the led and sensitivity button.

Typical Schneider web page. Missing any useful information. Use the manual for the SUA3000 - Page 9. https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=ASTE-6YWRZE_R1_EN.p...

On 9/12/2020 10:37 PM, Damian said:

Could you help me with these things?

 

https://pinoutguide.com/visual/gen/apc_smart_cable.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

Dear Brad
First of all, I apologize for the delay in my response.

Your help solved my problems.

I am very grateful for the time you took to help me.

Again, I thank you for help me.

Wish you a very happy new year.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

On 15/12/2020 8:59 PM, Damian said:

First of all, I apologize for the delay in my response.

Your help solved my problems.

Brilliant. Thanks for coming back to say so. Many people don't come back with a "that worked", so this makes it useful for others in the future. Glad I could help.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore