Smart 3000VA power consumption

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart 3000VA power consumption
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
7
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 AM . Last Modified: ‎2024-03-15 04:19 AM

Smart 3000VA power consumption

Hello all

Could someone tell me how to find out the power consumption of this UPS please?

Thank you

David.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

If we assume the UPS is plugged in and no load is connected then it will be quite efficient, assuming your also using the network management card it should be sub 100-50 watts, but that's a bit of a guess.

-Gavan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

On 14/12/2020 4:13 PM, Gavan said:

sub 100-50 watts, but that's a bit of a guess.

Not far from the mark. I have an SUA3000 with power meters pre and post. On the whole the overhead of the UPS alone is sub 50W at 240V. It usually idles between 40 & 50W (within the margin of error of measurement anyway). Input - Output with a constant ~300W load through the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

When you say power consumption what do you mean?

The unit will charge the batteries at about 10% of it's total capacity, so the power consumption is about 290ish watts during that phase. We would call the difference between the input and the output it's power factor for some models that can be as high as 99.9% when running on mains power, it more based around losses in conversion rather than actual power consumption.

Other than that we'd need need to know exactly which model it is, what mode it's running in and what you mean exactly by power consumption. The amount of load attached also plays a part in the units efficiency, a big UPS with a small load will be less efficient that if the unit's VA rating is closer to the load.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

Hi Gavan

Thanks for your reply. And you have a good question.

I should probably have said 'energy consumption'. 

What I ultimately need is an idea of the amount of kWh the UPS will use per year.

The assumption would be that anything plugged into it would not fail so would never need charging. So the energy consumption would be the quiescent load of the UPS itself.

However I may have misunderstood how the UPS works and this assumption is unrealistic.

The model is this one: https://www.apc.com/shop/ro/en/products/APC-Smart-UPS-XL-Modular-3000VA-230V-Rackmount-Tower/P-SUM30...

Does that give you all the information you need to assist?

Thanks again!

David

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

If we assume the UPS is plugged in and no load is connected then it will be quite efficient, assuming your also using the network management card it should be sub 100-50 watts, but that's a bit of a guess.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

On 14/12/2020 4:13 PM, Gavan said:

sub 100-50 watts, but that's a bit of a guess.

Not far from the mark. I have an SUA3000 with power meters pre and post. On the whole the overhead of the UPS alone is sub 50W at 240V. It usually idles between 40 & 50W (within the margin of error of measurement anyway). Input - Output with a constant ~300W load through the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

Thanks both!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

What I eventually need is a thought of the measure of kWh the UPS will utilize every year. The presumption would be that anything connected to it would not bomb so could never require charging. So the energy utilization would be simply the tranquil heap of the UPS. Anyway I may have misconstrued how the UPS functions and this supposition that is unreasonable. 

walgreenslistens.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 AM . Last Modified: ‎2024-03-15 04:19 AM

Hi 

I only have the power consumption at full load which is 142W.  

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore