Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
Hello forum,
I have an old Smart-UPS 3000 rackmount, model SU3000RM3U. It had apparently been in disuse for a long time, and the completely dead batteries have just been replaced. I have little experience with this model UPS, but it seems to be acting strange. So far, I have not tried to establish communications with the UPS serial port.
1) On-line LED flashing:
The strange thing here is the on-line LED never stops flashing. Does this mean the UPS is stuck in the self-test?
1.1) After power failure and restore, on-line LED turns off, on-battery LED remains on:
This is also strange, right? Should the UPS switch back on-line after power is restored?
2) Power-off button is momentary only:
This sounds broken, right?
3) UPS cannot be cold-started:
Should cold-starting work with this model UPS? Could it be that this problem is related to the other problems, above?
Thanks for any tips! I'd love for this thing to keep my rack running during our frequent power blips.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
This does not sound right in any sense. If the UPS is in self test mode, you should have on battery solid and online LED flashing. From what you say, you only see an online LED flashing.
What command are you issuing to cold start the UPS? In my mind, cold start is when you remove the UPS from AC power and hold down the power button to start the UPS off it's own battery. Typically, the UPS beeps twice and you hold the power button down until the second beep where you let go/release.
This UPS also does not have bypass functionality.
Do you get any UPS status information during these conditions? Like when the online LED is flashing - does it report on battery, etc?
Can you do an alarm test with NUT? To verify all the front panel LEDs work properly?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
Update:
Spent the evening playing with NUT. While many of the management features worked fine, oddly, some of the above problems seem to permeate the serial management interface, as well.
1) On-line LED flashing:
On-line LED continues to flash. Maybe this is normal?
2) Power-off commands:
Power-off commands don't work while utility power is applied. This includes commands listed as 'dangerous' in the documentation that can turn off loads in any circumstances.
The same power-off commands *do* work if utility power is removed.
When power is re-applied, the UPS comes back on-battery and powers up the loads, as hoped. However,
1.1) After power failure and restore, on-line LED turns off, on-battery LED remains on:
The UPS does not come on-line by itself. Manually issuing a NUT 'load.on' command does cause the UPS to switch back to utility power.
3) UPS cannot be cold-started:
Again, the UPS refuses to be cold-started from the serial interface, replying with "NO". Ha!
Sheesh! Can anyone shed some light on 1.1) above? I'm just mystified.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:58 AM . Last Modified: 2024-03-12 04:51 AM
This does not sound right in any sense. If the UPS is in self test mode, you should have on battery solid and online LED flashing. From what you say, you only see an online LED flashing.
What command are you issuing to cold start the UPS? In my mind, cold start is when you remove the UPS from AC power and hold down the power button to start the UPS off it's own battery. Typically, the UPS beeps twice and you hold the power button down until the second beep where you let go/release.
This UPS also does not have bypass functionality.
Do you get any UPS status information during these conditions? Like when the online LED is flashing - does it report on battery, etc?
Can you do an alarm test with NUT? To verify all the front panel LEDs work properly?