Smart-UPS 3000 XL Battery capacity issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 XL Battery capacity issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
2
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

Smart-UPS 3000 XL Battery capacity issue

I just installed a Smart-UPS 3000 XL with a battery pack.  At first it had 1:30 of runtime.  I did a Runtime callibration and it said completed after a few hours but battery capacity still continues to decrease.  It got down to 4% capacity and bounced between 4-5%.  I did a Self test and it seemed to raise the capacity a few percentage points but imediately started decreasing again.  I did a few self tests and got it up to 46% but now down to 26%.

Has anybody seen this before and if so what do you recommend

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
0
1337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

Battman covers it, check for the float charge of 54.65 volts (Should be 54 volts +/- .5V)

I have a SU3000NET that had a bad battery from the set of four batteries, caused infinite problems.

Also, does the unit run the fan when the battery is low?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
0
1337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

Some questions:

1. Does the UPS know that it has the external battery pack attached ? (this has to be programmed, either via the web interface if you have a management card, or with the "Battpack.exe" on floppy )

2. How old are the batteries and how long ago was the last calibration done or was one ever done ? ( that date is also available via web interface/management card)

I've never heard of anyone doing multiple self tests in succession but maybe it is kickstarting the UPS charging circuits briefly...but if the ups doesn't know it has an external pack, or if the UPS' battery constant is out of whack that could be causing issues, or there could be a weak battery cell or two in the string.

If there is a weak/dying battery in one or two of the indivudual RBC105 modules (is it an SUA3000 RM Smart UPS XL ?) it would badly drag down the battery string voltage at the UPS and that would be seen as lower charge %.

One or two checks you could physically do are:

Disconnect the external battery pack and see if the charge level starts rising or goes back to normal - that would point to the external pack being bad.

You could also disconnect the battery modules individually (will be three if its a rack mount with external SUA48 pack ) and test the voltage across that module's battery connector. A fully charged module should read around 50.5 volts DC....a discharged module would be hovering around 48 volts DC. A module with a bad cell would read less...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:46 AM

Battman covers it, check for the float charge of 54.65 volts (Should be 54 volts +/- .5V)

I have a SU3000NET that had a bad battery from the set of four batteries, caused infinite problems.

Also, does the unit run the fan when the battery is low?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore