Smart-UPS 2200INET - how to restore runtime after battery replacement?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200INET - how to restore runtime after battery replacement?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
4
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

Smart-UPS 2200INET - how to restore runtime after battery replacement?

Hi, I have this UPS and have just replaced the batteries as the old ones were bad. I ran the runtime calibration procedure but the UPS stopped it too soon (there was still 48.6V on the batteries), so it still shows 4 minutes runtime at 48.8% load, which was probably true with the old batteries, but I have new ones now and they even are a bit bigger (20Ah instead of 18Ah).

Last time I replaced the batteries I pulled the plug out of the wall socket and let the UPS discharge completely and shut down (because I wanted to see how long can it last with the new batteries), after that, the UPS probably displayed the correct runtime. However, the reason I have a UPS is so that I do not have to switch off my computers even when the power fails (for a short enough time) and I do not want to switch them off just to restore the runtime indicator.

I searched on Google and found out that it is possible to change the battery constant and then run the calibration and it should work OK, however, I could not find the constant for my UPS.

So, does anyone know the constant for my UPS or some way of calibrating the runtime that does not involve switching off the load?

(Just minor nitpicks about my UPS in general - why does the runtime calibration stop when the UPS thinks that there is 25% of battery capacity remaining, why not discharge the battery completely? Also, the fan turns on only when the batteries are charging or the UPS runs from the battery, so if it's 35C in the room the UPS gets quite hot and this shortens the battery life).

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • battery
  • runtime
  • smart-ups
  • ups
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

Thanks, the instructions in the PM helped.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

Hi, I have this UPS and have just replaced the batteries as the old ones were bad. I ran the runtime calibration procedure but the UPS stopped it too soon (there was still 48.6V on the batteries), so it still shows 4 minutes runtime at 48.8% load, which was probably true with the old batteries, but I have new ones now and they even are a bit bigger (20Ah instead of 18Ah).

Last time I replaced the batteries I pulled the plug out of the wall socket and let the UPS discharge completely and shut down (because I wanted to see how long can it last with the new batteries), after that, the UPS probably displayed the correct runtime. However, the reason I have a UPS is so that I do not have to switch off my computers even when the power fails (for a short enough time) and I do not want to switch them off just to restore the runtime indicator.

I searched on Google and found out that it is possible to change the battery constant and then run the calibration and it should work OK, however, I could not find the constant for my UPS.

So, does anyone know the constant for my UPS or some way of calibrating the runtime that does not involve switching off the load?

(Just minor nitpicks about my UPS in general - why does the runtime calibration stop when the UPS thinks that there is 25% of battery capacity remaining, why not discharge the battery completely? Also, the fan turns on only when the batteries are charging or the UPS runs from the battery, so if it's 35C in the room the UPS gets quite hot and this shortens the battery life).

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

That's a bit of a problem - there is no APC office in Lithuania, international phone calls cost a lot, but more importantly I cannot really speak English - I can write, read and understand the language quite well, but speaking it is a problem.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

I found this sticker near the top of the back of the UPS, above the fan. Maybe there is another one, I didn't see it.

I took a photo of the sticker:
!http://img571.imageshack.us/img571/793/dsc00612t.jpg!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Pentium100_apc
Ensign Pentium100_apc
Ensign

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

Thanks, the instructions in the PM helped.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of