Powerchute Business Edition not shut down the server due to power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Business Edition not shut down the server due to power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
3
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

Powerchute Business Edition not shut down the server due to power failure

Hi,

I have recently installed and configured APC PowerChute Business Editon 7.0.4 on the server. The server is connected to the Samrt UPS SC 1500 via Smart signalling.

Yesterday we received the alert saying the UPS is on battery, Immediately server was shutdown unexpectedly due to power failure. The configuration on the Powerchute Business Edition agent is When Power fails begins shutdown procedure 'at run time'

Why the APC Powerchute Business Edition didn't shutdown the server gracefully.

Attached the system and application logs from the server

Regards,
Anu

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

yes, its compatible. here is the compatibly chart for your review ->http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R24_EN.pdf

something else that also came to my attention was the possible incompatibility between the power supply on your server and the step approximated sinewave of the Smart UPS SC.

you can try the new software if you want but it also may be helpful to remove the data cable and software out of the picture and just try a pull plug test with the UPS and server. that may be an issue and you may require a pure sine wave UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

Hi,

I'm using Windows server 2003 R2 SP2 32 bit. Is the PowerChute Business Edition9.0 is compatiable with Windows server 2003? Also Attached the screenshot for Shutdown configuration on theserver

Regards,
Anu

Message was edited by: anandas

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

what operating system did you install this on? may I ask why you installed 7.0.4 when we are currently on and supporting powerchute business edition 9.0?

i would suggest uninstalling 7.0.4, especially if you are using a newer OS, and installing 9.0, available at http://www.apc.com/tools/download/index.cfm.

also, let us know the OS and then see if you can provide any details from the agent as far as what events you have configured to shutdown with screen shots. i am not sure what event you configured based on "*The configuration on the Powerchute Business Edition agent is When Power fails begins shutdown procedure 'at run time'*"

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

0 Likes
0
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:38 AM

yes, its compatible. here is the compatibly chart for your review ->http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R24_EN.pdf

something else that also came to my attention was the possible incompatibility between the power supply on your server and the step approximated sinewave of the Smart UPS SC.

you can try the new software if you want but it also may be helpful to remove the data cable and software out of the picture and just try a pull plug test with the UPS and server. that may be an issue and you may require a pure sine wave UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore