Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Smart UPS 2200 stopped working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 2200 stopped working
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:42 AM . Last Modified: ‎2024-03-15 06:14 AM

0 Likes
3
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:42 AM . Last Modified: ‎2024-03-15 06:14 AM

Smart UPS 2200 stopped working

hello all, 

I checked the ups and found that R38 and R43 connected with the drain of 2N7000 mosfet got burnt and replaced burnt resistor and F3.Then the Ups energized and started working 

but still the Resistances 38 and 43 (1K 1/4 watts ) are getting hot. What may be the possible reason.Please check the attachment and refer sheet number 3 for detailed circuit 

Resistors R38 and R43 are getting hot  only during standby/charging operation and resistors are normal during ups backup on condition. 

Thanks   

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

0 Likes
0
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

Yes, the 3.x & 4th gen units (late black faced SU and all SUA and above) don't have this issue as they use a dedicated high side driver for the MOSFET bridge rather than the discrete bootstrap driver which has this flaw.

When I bought my first 2200 the resistors had gone, taken out both high side drivers which then turned on both sides of the bridge simultaneously and destroyed half the MOSFETS. Oddly enough it didn't damage the fuse, just most of the driver transistors and the MOSFETS.

It did sound impressive when it went bang though and let a lot of magic smoke out. Put higher power rated resistors in, give them room to breathe and keep them away from the other components and it'll probably be ok.

I did a battery calibration on a 2200 last week, and after 2 hours (it has an extra 55ah of external battery) at a 1KW resistive load I realised the fan had died, the internal temp was >65C and it smelt a bit funny. A new fan and a bit of a once over and it's good as gold. These units are very well designed and solidly built.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 09:42 AM . Last Modified: ‎2024-03-15 06:14 AM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:42 AM . Last Modified: ‎2024-03-15 06:14 AM

That's "normal" behaviour for the old 3rd generation 48V units. Replace them with 1W resistors and stand them off the board. I found a resistor at RadioSpares (RS) with small enough leads that fit through the holes in the board but it was a bit of a search.

if you are replacing parts, replace bootstrap caps C34 & C35 while you are in there. They get exposed to quite some heat and tend to dry out. They're not critical, but I've never found any that are close to spec after 10 years.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

Thanks Brad for the quick response.i found the F3 fused and used a thin wire to test and the unit is functional. Only during charging the resistors 1K are heating up.

I don’t know which generation is the ups .The model number is YS 0139121473 and as per the model number the product is manufactured on 2001 39th week 

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

0 Likes
0
981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:43 AM . Last Modified: ‎2024-03-15 06:14 AM

Yes, the 3.x & 4th gen units (late black faced SU and all SUA and above) don't have this issue as they use a dedicated high side driver for the MOSFET bridge rather than the discrete bootstrap driver which has this flaw.

When I bought my first 2200 the resistors had gone, taken out both high side drivers which then turned on both sides of the bridge simultaneously and destroyed half the MOSFETS. Oddly enough it didn't damage the fuse, just most of the driver transistors and the MOSFETS.

It did sound impressive when it went bang though and let a lot of magic smoke out. Put higher power rated resistors in, give them room to breathe and keep them away from the other components and it'll probably be ok.

I did a battery calibration on a 2200 last week, and after 2 hours (it has an extra 55ah of external battery) at a 1KW resistive load I realised the fan had died, the internal temp was >65C and it smelt a bit funny. A new fan and a bit of a once over and it's good as gold. These units are very well designed and solidly built.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of