Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS 2200 - inverter DC imbalance during self test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 - inverter DC imbalance during self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

0 Likes
3
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

Smart-UPS 2200 - inverter DC imbalance during self test

Hello,

during christmas "Murphy" visited us.

One of our 6 UPS shut down after it started a self test.

Today I've tried to understand what happens, but I don't know how I can fix the problem.

I can cause the same problem again: I have to start a manual self test, then I receive the following messages from the UPS:

email messages

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:19:11

Code: 0x0137

Informational - UPS: Started a self-test.

Serial # : BA0826021420

Device Ser #: NA

Date: 12/30/2013

Time: 14:19:23

Code: 0x0114

Critical - UPS: The output power is turned off.

Serial # : BA0826021420

Device Ser #: NA

Date: 12/30/2013

Time: 14:19:27

Code: 0x0106

Critical - UPS: Refused a self-test; UPS is overloaded.

... here I've turned the UPS off and on again (the lights in the front side flashed) ...

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0137

Informational - UPS: Started a self-test.

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0113

Informational - UPS: The output power is now turned on.

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0139

Informational - UPS: An inverter DC imbalance no longer exists.

Do I need to replace the whole UPS?

Regards

Tino

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

Good morning,

I do think it is likely you'll need to replace the entire UPS (under warranty or on your own via purchase or trade in) or have it repaired if that service is available in your region. This UPS does not have any components that are designated to be replaced besides the battery module unfortunately. It sounds like a problem with the inverter. Considering the UPS is not all that old based on the serial number, what is the load attached you mention? Networking gear, servers, etc? I don't think its possible based on what you've said so far but premature failures can be sometimes be related to the type of load attached or even the input feeding the UPS.

If you want to try a reset, you could do that. I think it is very unlikely it will change the situation but it is worth a try I suppose. To do that though, you need to turn off and remove any attached load on the UPS itself. Then, turn off the UPS itself and disconnect any data cables (sounds like though you only have the ethernet cable connected to a UPS Network Management Card though and no USB or serial cables - you could leave that). Then, remove the UPS from AC power and hold the off button (o) for several seconds and you should see the front panel LEDs flash and/or hear an audible click. Once this happens, reconnect the UPS to AC power and turn it back on and reconnect your attached load (if you wanted) and also check the status on the management card. The UPS does a self test when it turns back on so you could see if it does it then. In reality, I guess if there is any change, I'd still keep an eye on this but I don't know if I'd fully trust it anyway.

Also, if you want, we can take a further look at the data/event logs from the UPS Network Management Card (I shouldn't need config.ini or any of the others). Please note the data log will be erased though if the Network Management Card is power cycled so you can get those before you try the reset above if you choose to do it. Instructions are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

P.S. - the reset instructions above assume you're using something similar to an SUA2200 (per the model prefix on the white sticker on the rear of the UPS) so if the model SKU does not start with SUA, let me know. Reset instructions would be a little different.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

Hello,

during christmas "Murphy" visited us.

One of our 6 UPS shut down after it started a self test.

Today I've tried to understand what happens, but I don't know how I can fix the problem.

I can cause the same problem again: I have to start a manual self test, then I receive the following messages from the UPS:

email messages

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:19:11

Code: 0x0137

Informational - UPS: Started a self-test.

Serial # : BA0826021420

Device Ser #: NA

Date: 12/30/2013

Time: 14:19:23

Code: 0x0114

Critical - UPS: The output power is turned off.

Serial # : BA0826021420

Device Ser #: NA

Date: 12/30/2013

Time: 14:19:27

Code: 0x0106

Critical - UPS: Refused a self-test; UPS is overloaded.

... here I've turned the UPS off and on again (the lights in the front side flashed) ...

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0137

Informational - UPS: Started a self-test.

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0113

Informational - UPS: The output power is now turned on.

Serial # : BA0826021420

Device Ser #: JS0819001446

Date: 12/30/2013

Time: 14:21:05

Code: 0x0139

Informational - UPS: An inverter DC imbalance no longer exists.

Do I need to replace the whole UPS?

Regards

Tino

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

I've forgotten ... the normal load of the UPS is 45-50% 😉

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:24 AM . Last Modified: ‎2024-03-12 04:30 AM

Good morning,

I do think it is likely you'll need to replace the entire UPS (under warranty or on your own via purchase or trade in) or have it repaired if that service is available in your region. This UPS does not have any components that are designated to be replaced besides the battery module unfortunately. It sounds like a problem with the inverter. Considering the UPS is not all that old based on the serial number, what is the load attached you mention? Networking gear, servers, etc? I don't think its possible based on what you've said so far but premature failures can be sometimes be related to the type of load attached or even the input feeding the UPS.

If you want to try a reset, you could do that. I think it is very unlikely it will change the situation but it is worth a try I suppose. To do that though, you need to turn off and remove any attached load on the UPS itself. Then, turn off the UPS itself and disconnect any data cables (sounds like though you only have the ethernet cable connected to a UPS Network Management Card though and no USB or serial cables - you could leave that). Then, remove the UPS from AC power and hold the off button (o) for several seconds and you should see the front panel LEDs flash and/or hear an audible click. Once this happens, reconnect the UPS to AC power and turn it back on and reconnect your attached load (if you wanted) and also check the status on the management card. The UPS does a self test when it turns back on so you could see if it does it then. In reality, I guess if there is any change, I'd still keep an eye on this but I don't know if I'd fully trust it anyway.

Also, if you want, we can take a further look at the data/event logs from the UPS Network Management Card (I shouldn't need config.ini or any of the others). Please note the data log will be erased though if the Network Management Card is power cycled so you can get those before you try the reset above if you choose to do it. Instructions are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

P.S. - the reset instructions above assume you're using something similar to an SUA2200 (per the model prefix on the white sticker on the rear of the UPS) so if the model SKU does not start with SUA, let me know. Reset instructions would be a little different.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore