Smart UPS 2200 INET battery bleeper disable and recalibrate?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 2200 INET battery bleeper disable and recalibrate?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:49 AM

0 Likes
3
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:49 AM

Smart UPS 2200 INET battery bleeper disable and recalibrate?

Hi

I have purchased a smart ups from eBay, i have also got the com and the smart slot enabling me to interface it via Ethernet. I cannot turn of the battery bleeper and seem to have limited options. I had the SU1000i which has a lot more options than this and easier to operate. I also having problems with battery's seem to go flat. Is there a way i can calibrate battery and turn off the bleeper via Ethernet? if so which program to use i'm using power chute business. i also have compatibility issues with older versions I'm running windows 7 x64

many thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

Sounds like normal behavior - that's just the UPS' low battery alert. If as you say there is a management card in the slot in the back you can change the on-battery behavior to Mute the alert.

As for calibration you can either do it thru the management card, or do it manually by "BRAIN-DEADING" the UPS:  Pull the plug when its on line with load attached then let the UPS completely drain its batteries til it shuts down, then unplug the UPS, press and hold the off button til you hear a click, then disconnect the battery, press and hold the power on button for 20 to 30 seconds to discharge the UPS' internal capacitors, then plug the battery back in, plug the UPS back in and power it up. As it charges up again the battery run time should be recalibrated.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

Hi,

Are you saying that with the UPS plugged in, and the batteries connected, the batteries do not appear to be charging ? (IE battery bar graph indicators - all five - are not illuminated even after 24 hours of charging ?

And...by "bleeper" do you mean the UPS front panel "replace battery" LED or the "fault" LED is lighted up and the UPS is beeping every few seconds ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

No what I am saying is the battery's charge as normal. When load is connected say 300w it will run once the ac is unplugged, after about 1 minute i lose the first bar of battery, after 10 minute i lose the second bar, in about another 10 or 20 min I am down to 1 bar. From that point the bleeper constantly bleeps, which is annoying. But the battery's are still good for another 2 hour or so. Maybe longer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:45 AM . Last Modified: ‎2024-03-12 02:48 AM

Sounds like normal behavior - that's just the UPS' low battery alert. If as you say there is a management card in the slot in the back you can change the on-battery behavior to Mute the alert.

As for calibration you can either do it thru the management card, or do it manually by "BRAIN-DEADING" the UPS:  Pull the plug when its on line with load attached then let the UPS completely drain its batteries til it shuts down, then unplug the UPS, press and hold the off button til you hear a click, then disconnect the battery, press and hold the power on button for 20 to 30 seconds to discharge the UPS' internal capacitors, then plug the battery back in, plug the UPS back in and power it up. As it charges up again the battery run time should be recalibrated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore