Smart-UPS 2200 - Error Messages

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 - Error Messages
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
7
3745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

Smart-UPS 2200 - Error Messages

We have a number of Smart-UPS 2200 in production. Manufacture date is Sept. 2011

This morning, we received 4 error messages (all have the same time and date stamp) on 3 separate UPSs:

01/03/2013 05:13:40 UPS: The battery power is too low to support the load; if the power fails, the UPS will be shut down immediately.
01/03/2013 05:13:40 UPS: A discharged battery condition no longer exists.
01/03/2013 05:13:40 UPS: On battery power in response to unknown
01/03/2013 05:13:40 UPS: No longer on battery power.

Am I looking at bad batteries here?

Thanks,
Tom

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

Here are the files you requested.

Thanks,
Tom

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

not necessarily. what is your total runtime with load attached? what is your low battery duration set to? (i believe that is under UPS tab->General or at least somewhere under UPS tab in the management card).

i think what happened is the UPS went to battery and the available runtime came within two minutes of your low battery duration setting (which by default is two minutes). if it was changed, it could have caused this sequence of events.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

Thanks for your response.

Load in Watts = 16.9%
Runtime Remaining = 1 hour 4 min
Low Battery Duration = 2 minutes

Thanks,

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

hmm OK. can you get me the full logs. i also want to look at the data log at the time these came up.

i need event.txt and data.txt. you can remove any IP addresses or whatever that you don't want visible in the log files. instructions are here -> http://www.apc.com/site/support/index.cfm/faq/ -> search for FA156131

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

thanks. i assume you are aware of the unauthorized SNMP access attempts which are eating your log space...?

as far as the issue you presented, can you give me the firmware version of this UPS? it would be under UPS->About. i am thinking it is not up to date since it says "on battery due to unknown" which I know was addressed at some point so it does not say unknown.

the sequence of events does not look right to me and i cant tell if its happened previously (like during a self test even though it doesnt report it) because the log is spammed with the SNMP access attempts.

the data log reports that battery capacity went to 20% at some point. i am wondering if the 1 hr 4 minutes runtime you have is legit and if it dropped really low to two minutes on the quick battery blip you had and got to within 2 minutes of the low battery duration to generate those events.

have you witnessed an outage and saw how long the runtime on battery went for?

i am thinking if your firmware is outdated that we get that updated and see if it occurs again but i'd really try to address those unauthorized SNMP access attempts if possible so we can refer to the log history.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:10 AM . Last Modified: ‎2024-03-13 01:02 AM

Good morning -

The Firmware Revision is: UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0 (ID18)

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

ok - i believe you have a variety of SMT2200 (versus SMX2200). i am going by ID18.

what i would suggest we do is read through this article (http://www.apc.com/site/support/index.cfm/faq/ -> search for FA164737 and confirm that i am correct. or if you know the exact model, we can cross check.

essentially, i believe there is going to be an update available. i am guessing though that your UPS falls into this category:

Units that do not support firmware update via USB:
SMX Units earlier than UPS 07.2
SMT units earlier than UPS 08.0

this is one option (reading through and using this USB firmware update option) or once we confirm the model, we can try pushing the update via the NMC. you can FTP the image file (which we can extract from the firmware upgrade wizard mentioned in the article) and send it to the network management card and then have the network management card update the UPS. either way though, this will require the output of the UPS to be turned off during the upgrade. the upgrade shouldnt take more than 10 minutes from start to end though in my experience.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
3744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

Here are the files you requested.

Thanks,
Tom

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore