SURT10000XLT - CHARGER PROBLEM - FIXABLE?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT10000XLT - CHARGER PROBLEM - FIXABLE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

0 Likes
0
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:11 AM . Last Modified: ‎2024-03-13 01:02 AM

SURT10000XLT - CHARGER PROBLEM - FIXABLE?

Like many APC efficient designs of 10kVA and up; TWO DC Busses are used to feed the inverter, one for the +ve half and one for the -ve half. Each has an open circuit voltage of about 200 volts. The SURT10000XLT is no different.
We have a SURT10000XLT unit in the shop for evaluation to determine if this unit will become electronic junk or for some reasonable amount can be repaired. I don't see too many folks who have worked on this unit with postings. That probably just means that most said NAY NAY, I'm too tall for that product and made it junk right away.
I've had two units of this exact size fail badly in the last 6 months so I'm sure that I am not alone with problems on this unit.
Our unit conditions are: (1) unit must have battery connected to start up - 4 strings of 96 volts each (2) utility on and power switch on - turns fans on (3) Pressing 1 [test] button runs on battery for a bit and then goes to normal with top green sinewave LED on and a couple of battery LED'S illuminated (4)After the unit destroyed our NEW batteries, we have some used ones for this testing that are not fully charged, so the few battery LED's on seams normal.
We know that the unit is not normal however because one side of the charger is putting out nothing because the DC reading is the same as the open circuit voltage of the batteries, while the other side is putting out 235 volts - meaning that those batteries will soon explode or overheat at least. The charge voltage should be between 216 and 218 volts.
With what appears to be only ONE mother board for everything, the charger looks like it's on there too. The question is then - does anyone know besides the designer where the charger is, what to test next, are parts sold by APC, and whether it's just a $5000 junk box?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore