Hi
I have a lot of servers connected to 2 different APC RT6000 UPSes. (one powersupply to each UPS)
I want to configure shutdown of these servers only when both UPSes is running (low) on battery. How can this be done?
(if only one fails, or is low on battery, nothing should be shut down)
Not alot of experience with PCNS (or other APC software), th eonly setups I have done is with single UPS)
Hope someone can give me a good solution 🙂
HKA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:11 AM . Last Modified: 2024-03-13 01:02 AM
I would suggest installing PCNS on the server and selecting the redundant solution during the install. This would require each UPS having a network management card but based on the size of the UPS, they should include one. Do you have both Network management cards on your network? The link below shows installation instructions for PCNS which includes redundant solutions.
http://www.apcmedia.com/salestools/PMAR-8RNKEY_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:11 AM . Last Modified: 2024-03-13 01:02 AM
I would suggest installing PCNS on the server and selecting the redundant solution during the install. This would require each UPS having a network management card but based on the size of the UPS, they should include one. Do you have both Network management cards on your network? The link below shows installation instructions for PCNS which includes redundant solutions.
http://www.apcmedia.com/salestools/PMAR-8RNKEY_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of