Does anyone know of a way to update the default notifications from 2mins I'd like to update to 30mins. I have four different email notifications that are all set to be notified in 2 min intervals.
I did start to do it manually but there are too many.
Thanks Steve
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 PM . Last Modified: 2024-03-14 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 PM . Last Modified: 2024-03-14 02:58 AM
Thanks doing by Group worked.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 PM . Last Modified: 2024-03-14 02:58 AM
Mass setting of your notification intervals for events can be done in the Network Management Card by going to the Administration -> Notifications tab, then -> Event Actions "By Group". Here you can set categories of events, or severity levels of events, to all have the same settings you desire. This will allow you to set several, if not dozens of events under that same category to have 30m. notification times.
Of course, the manual way I assume you are describing is the Event Actions "By Event" section, which allows you to set individual events for different settings. I hope this all answers your question.
Keep in mind that I am basing this information off a 1st generation NMC (AP9617, 9619, etc.) or a 2nd generation NMC (AP9630, etc.), and the most up to date firmware for the NMC.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 PM . Last Modified: 2024-03-14 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 PM . Last Modified: 2024-03-14 02:58 AM
Thanks doing by Group worked.