Smart-UPS 1500 - won't start after the grid is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 - won't start after the grid is restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
fpavel
fpavel
Cadet

Posted: ‎2023-12-24 02:13 AM

0 Likes
6
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-24 02:13 AM

Smart-UPS 1500 - won't start after the grid is restored

Hi, I operate SMC1500I-2UC in our SMB, the unit is still under warranty and the battery is working well. The problem is, once the rack is powered by the battery (the grid is down), when the battery runs out and the UPS switches off, even after restoring the grid power, the UPS won't automatically switch on and I have to go on-site and switch it manually ON.

 

Is this expected with this model or it should automatically switch ON once power is restored? The UPS is not managed by any other control software, it is just connected to SmartConnect without a subscription.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Kirk Teken
Kirk

Posted: ‎2024-01-05 02:48 PM

0 Likes
1
3345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-05 02:48 PM

Assuming you still have access to SmartConnect I would see if there is an option to select the operational state. Most of the APC UPS's have the option to define how the UPS should behave upon power restore. You would of course select the option to have the UPS turn back on once 120 VAC was restored. If there is no option available in the SmartConnect portal I would suggest you install Power Chute Business Edition and connect the UPS to a computer system.

 

There should be power option within the Power Chute software to define the above option.

Reply

Link copied. Please paste this link to share this article on your social media post.

fpavel
fpavel
Cadet

Posted: ‎2024-01-16 02:13 AM

0 Likes
3
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 02:13 AM

I do have access to the PowerChute Business Edition, but what exactly should I focus on? I don't see any settings that are related to what should happen after the power is restored.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-01-16 05:07 AM

In response to fpavel
0 Likes
2
3287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 05:07 AM

Depending upon version of software it should be under Configuration -> Shutdown -> On Battery Behaviour -> Restart when power restored. 

Reply

Link copied. Please paste this link to share this article on your social media post.

fpavel
fpavel
Cadet

Posted: ‎2024-01-16 05:58 AM

In response to Teken
0 Likes
1
3280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 05:58 AM

The version is PowerChute Business Edition Agent Version10.0.5.301. Below are screenshots from the settings. Can you see if something is wrong with the settings? 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-01-16 06:34 AM

In response to fpavel
0 Likes
0
3236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 06:34 AM

In the third image provided by you it shows the UPS is programmed to turn back on once AC power is restored. Which is what you want so that’s good. At the very bottom you have a 8 second delay on the output so changed that to 0 seconds.

 

Keep in mind none of this will address other possible faults / problems that may exist. Generally speaking you should test and validate for these behaviours:

 

Power On - No Battery: Disconnect the battery from the UPS while it’s running. Unplug the AC line wait 30 seconds. Plug the AC line back in. Does the UPS turn back on without the attached battery? If yes good. If no, this is how the UPS is designed.

 

Next step to verify: Unplug the AC line. Attach the battery cartridge. Plug the AC line back in. Does the UPS turn back on once the battery is attached? If yes good, which means there must be a connected battery for the UPS to turn back on. If the answer is no, the UPS does not turn back on and requires a user to press the power on button that is by design.

 

Test the above scenario and let us know. Keep in mind these tests also don’t address a weak battery, over loaded outlet, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2024-01-16 01:22 PM

In response to Teken
0 Likes
0
3263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 01:22 PM

@Teken 

 

If the UPS turns off because the batteries have drained to zero or close to zero, the UPS will not power on without user intervention. This is by design. If you want the UPS to power on automatically when the AC is restored, configure it to turn the outlet groups off before the batteries are drained. You can do this through PowerChute or via the UPS LCD panel. 

 

In PowerChute go to Outlet Sequencing. Via the LCD panel go to Configuration, Config Main Outlet Group, Load Shedding, and do the same for Outlet Group 1. 

 

NOTE: configuration of the outlet groups via the LCD panel is only available on the SMT when the configuration menu is set to advanced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore