Hi,
I'm trying to use an APC Smart UPS 1500 connected on an USB port, in conjunction with Vmware Management Assistant and PoweChute Business Edition in order to protect two Vmware hosts.
vMA detects the UPS at boot time (see the logs bellow) but, following the installation of pbeagent, no matter which port I chose for the communication, the tool reports "UPS communication lost".
I tried to specify /dev/usb/seups0, /dev/usb/hiddev0 or /dev/hidraw0 as communication ports but no change. The UPS has a RJ45 port in the back.
Any idea what I'm missing here?
Thanks,
Daniel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:30 AM . Last Modified: 2024-03-18 12:25 AM
Hi,
PowerChute Business Edition does not support USB comm to UPS while running on VMware vMA. PowerChute does support comm between the vMA and UPS over serial. See the PowerChute 9.5 installation guide and the User's Guide for assistance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:30 AM . Last Modified: 2024-03-18 12:25 AM
Hi,
PowerChute Business Edition does not support USB comm to UPS while running on VMware vMA. PowerChute does support comm between the vMA and UPS over serial. See the PowerChute 9.5 installation guide and the User's Guide for assistance.