Smart-UPS 1500 XLM with a critical alarm

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 XLM with a critical alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:43 AM

0 Likes
5
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:43 AM

Smart-UPS 1500 XLM with a critical alarm

Hello,

I have a 1500XLM UPS and it generated a critical alarm with the following message: Local Management-To-NMC Integrated EM Sensor Communication Lost: Int Sensor at Int Sensor Loc

When I go into Environtment -> Temp & Humidity page, it's not showing me any information and just shows the critical alarm.

Does this mean that the sensor is dead? Is there any way to reset the sensor?

The UPS is running in the production network so issuing a downtime is not favorable.

Thanks in advance.
YJ

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

under normal circumstances, no. make sure not to bump any plugs in the back of the UPS though πŸ™‚

Edit: I guess I should indicate that the PROPER removal/insertion procedure for any smart slot accessory would be to power down the UPS in brain dead it, according to [this article|http://nam-en.apc.com/app/answers/detail/a_id/10865]. it indicates SU or SUA smart ups but SUM is the same.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

can you please let us know what model network management card you have? check the administration tab, general, about and it will say. also tell us what AOS and APP versions you have from there. if it is AP9619, most likely the daughterboard that provides environmental information has become separated the main board.

i would go physically over to the card, ensure the PS/2 probe is attached, and then remove the card from the UPS and push the two boards together. there is a single white connector that holds them together that you should see. then reseat the card into the slot and see what you get. if that does not solve the issue and you are confident that the boards are securely pushed together, we will have to investigate further.

if it is AP9631, this can happen when the probe is disconnected from the Universal Input/Output jack, which is an RJ-45 style. ensure that it did not become lose or unplugged.

let us know what you find πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

Hello!

This is what i found from the web interface:

Model Number: AP9619
Hardware Revision: A10

APC OS (AOS):
Name: aos
Version: v3.6.1

Application Module:
Name: sumx
Version: v3.5.8

I will try your method tomorrow and let you know how it goes!

Thank you for your prompt response
Regards,
Yj

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

ok, great. you are one revision behind so if you want to upgrade, you'll see SFSUMX372 on the website to download under Software & Firmware.

ill check back tomorrow to see how you made out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

Hi!

I haven't tried fixing it because the UPS turned out to be in a room where i needed special access. I will try fixing it later this week or next week, and let you know how it goes.

One more question though: If i follow your method the UPS won't turn off or switches lose their power, right? As I mentioned in my original post, the UPS is installed in the production network so I got to be careful.

Thank you very much for your help!
Much appreciated πŸ˜ƒ

Regards,
YJ

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:20 AM . Last Modified: β€Ž2024-03-13 05:42 AM

under normal circumstances, no. make sure not to bump any plugs in the back of the UPS though πŸ™‚

Edit: I guess I should indicate that the PROPER removal/insertion procedure for any smart slot accessory would be to power down the UPS in brain dead it, according to [this article|http://nam-en.apc.com/app/answers/detail/a_id/10865]. it indicates SU or SUA smart ups but SUM is the same.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore