Recommended Load on Smart-UPS 1500RM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Recommended Load on Smart-UPS 1500RM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
2
2783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

Recommended Load on Smart-UPS 1500RM

First post here,

I've inherited the job of looking after the network here and in our rack we've got a Smart-UPS 1500RM that currently has plugged into it - 2x 48-port switches, a Cisco ASA-5510 firewall, a Barracuda Message archiver (small 1U firewall-sized device), an IBM DS4700 SAN with 13 SCSI drives, a Dell Poweredge 2U Rack mount server and a 17" LCD monitor.

We are going to be adding another 2U Dell rackmount server for our backups, and I am concerned with putting too much load onto the UPS. The load is currently at 60% judging from the lights on the front. The last time I needed to add one of the switches and was out of plugs on the UPS, the guy who originally installed the UPS said to just add a 16-plug power bar to give me more outlets.

My question is, how can you judge when you've got too much plugged into one UPS and it's time to add another UPS into the mix? Is there some rule of thumb that is used?

Much appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

So if I read the manual correctly, 3 of 5 lights on the front indicate 50% load currently, which of course affects the runtime. Judging by what I already have, I don't think that adding a 2U rackmount server will reduce the runtime by too much, but does the UPS actually monitor the current being drawn? I just don't want to power up the server and end up tripping a breaker somewhere because I'm drawing too much current on the same circuit, and end up killing power to all that equipment. I'm hoping for someone with some server rack experience to give me what they would consider to be a reasonable load on a UPS before they would add an additional one.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

generally, at APC, we recommend no more than 80% load. that helps you account for in rush current or a little extra power draw during peak usage times on your equipment but under normal circumstances, 80% what you should see.

you need to keep in mind your required runtime. a power bar (PDU) may give you more outlets but it certainly does not add to the watts/VA capacity of the UPS. the UPS can become overloaded of course with too much load and it could possibly turn off of or be running at 100% and then when a power outage occurs, it will provide far less runtime than you probably desire.

ultimately, i think you need to find out how much more power the server you want to add will draw and then lets calculate that into what you currently have.

i assume you are not using an powerchute software or UPS Network Management Card with this device so we can log in and see the exact load percentage on the unit? in the user's manual here, it tells you about the load bar graph on the front that you estimated.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:20 AM . Last Modified: ‎2024-03-13 05:43 AM

So if I read the manual correctly, 3 of 5 lights on the front indicate 50% load currently, which of course affects the runtime. Judging by what I already have, I don't think that adding a 2U rackmount server will reduce the runtime by too much, but does the UPS actually monitor the current being drawn? I just don't want to power up the server and end up tripping a breaker somewhere because I'm drawing too much current on the same circuit, and end up killing power to all that equipment. I'm hoping for someone with some server rack experience to give me what they would consider to be a reasonable load on a UPS before they would add an additional one.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore