Smart UPS 1500 X Randomly Shuts Down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1500 X Randomly Shuts Down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:25 AM

0 Likes
6
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:25 AM

Smart UPS 1500 X Randomly Shuts Down

I have a Smart UPS 1500 X (SMX1500RM2UNC) with one external battery pack (SMX48RMBP2U) that just powered down all the outlet groups for no apparent reason.  

The unit is not that old, it's been in service since December 2016 (manufacture date is October 2016).  The load on it is rather low, 25%-30%.

Early this morning it appeared to be switching rapidly between shutting down and powering up:
----------------
06/03/2018 09:01:56 Device UPS: The output power is now turned on. 0x0113
06/03/2018 09:01:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 09:01:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 09:01:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 09:01:50 Device UPS: The output power is turned off. 0x0114
06/03/2018 09:01:50 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 09:01:50 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 09:01:50 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 09:01:50 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 09:01:50 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 09:01:50 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 09:01:50 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:25:27 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:25:27 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:25:27 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:25:27 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:25:21 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:25:21 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:25:21 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:25:21 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:25:21 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:25:21 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:25:21 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:25:21 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:18:37 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:18:37 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:18:37 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:18:36 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:18:32 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:18:32 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:18:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:18:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:18:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:18:29 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:18:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:18:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:18:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:18:24 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:18:24 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:18:23 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:23 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:18:23 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:23 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:18:23 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:18:23 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:18:02 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:18:01 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:18:01 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:18:01 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:17:56 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:17:56 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:17:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:17:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:17:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:17:41 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
06/03/2018 07:17:28 Device Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. 0x0344
06/03/2018 07:17:26 System Network service started. IPv6 address FE80::2C0:B7FF:FEDA:1ECA assigned by link-local autoconfiguration. 0x0007
06/03/2018 07:17:24 System Network service started. System IP is 10.5.0.15 from manually configured settings. 0x0007
06/03/2018 07:17:19 System Network Interface restarted. 0x0002
06/03/2018 07:17:12 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:17:12 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:17:11 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:11 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:17:11 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:11 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:17:11 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:17:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:17:02 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:17:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:17:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:17:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:16:57 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:16:57 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:16:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:16:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:16:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:16:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:16:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:16:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:15:19 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:15:19 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:15:19 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:15:19 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:15:13 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:15:13 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:15:13 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:15:13 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:15:13 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:15:13 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:15:13 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:15:07 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:15:07 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:15:07 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:07 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:15:07 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:07 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:15:07 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:15:07 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:15:05 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:15:05 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:15:05 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:15:05 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:15:00 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:15:00 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:14:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:14:59 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:59 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:14:59 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:14:56 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:14:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:14:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:14:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:14:51 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:14:51 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:14:51 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:14:51 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:14:51 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:14:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:13:56 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:13:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:13:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:13:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:13:52 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:13:52 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:13:52 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:52 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:13:52 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:52 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:13:52 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:13:37 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:13:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:13:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:13:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:13:32 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:13:32 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:13:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:13:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:13:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:13:16 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:13:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:13:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:13:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:13:10 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:13:10 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:13:10 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:13:10 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:13:10 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:13:10 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:13:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:13:05 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:13:05 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:13:04 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:04 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:13:04 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:04 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:13:04 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:13:04 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:12:53 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:53 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:12:53 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:12:53 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:12:47 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:47 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:12:47 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:47 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:12:47 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:47 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:12:47 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:47 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:12:45 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:45 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:12:45 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:12:45 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:12:39 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:39 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:12:39 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:39 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:12:39 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:39 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:12:39 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:39 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:12:36 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:12:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:12:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:12:31 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:31 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:12:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:12:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:12:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:12:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:12:29 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:12:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:12:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:12:18 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:18 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:12:17 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:06 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:06 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:12:06 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:12:00 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:12:00 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:59 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:59 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:59 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:42 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:42 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:42 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:42 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:37 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:37 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:36 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:36 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:36 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:33 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:33 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:33 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:33 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:29 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:29 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:29 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:29 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:29 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:28 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:28 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:28 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:28 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:23 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:23 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:23 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:23 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:23 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:23 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:23 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:23 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:22 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:22 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:22 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:22 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:17 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:17 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:16 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:16 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:16 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:16 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:11 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:11 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:10 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:10 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:10 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:09 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:09 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:09 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:09 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:11:04 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:11:04 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:11:03 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:03 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:11:03 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:03 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:11:03 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:11:03 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:11:02 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:11:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:11:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:11:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:10:57 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:57 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:57 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:57 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:10:57 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:57 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:10:57 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:57 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:10:56 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:10:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:10:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:10:51 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:51 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:50 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:45 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:45 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:44 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:39 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:39 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:38 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:38 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:10:38 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:38 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:10:38 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:38 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:10:36 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:10:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:10:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:10:30 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:30 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:30 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:30 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:10:30 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:30 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:10:30 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:30 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:10:29 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:10:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:10:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:10:24 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:24 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:23 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:18 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:18 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:17 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:11 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:11 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:11 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:11 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:10:11 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:11 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:10:11 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:10:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:10:10 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:10:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:10:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:10:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:10:04 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:10:04 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:10:04 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:09:59 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:09:59 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:09:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:09:58 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:58 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:09:58 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:58 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:09:57 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:09:57 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:09:57 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:09:57 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:09:52 Device UPS: The output power is turned off. 0x0114
06/03/2018 07:09:52 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 07:09:51 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 07:09:51 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 07:09:51 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
06/03/2018 07:09:51 Device UPS: The output power is now turned on. 0x0113
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 07:09:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 07:09:46 Device UPS: The output power is turned off. 0x0114
-----------
I thought that was strange, I couldn't find any explanation for this.  Then this evening, it did it again!
----
06/03/2018 22:42:38 apc Web user 'apc' logged in from 10.5.0.196 [10.5.0.196]. 0x0015
06/03/2018 22:37:02 Device UPS: The output power is now turned on. 0x0113
06/03/2018 22:37:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
06/03/2018 22:37:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
06/03/2018 22:37:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
06/03/2018 22:36:57 Device UPS: The output power is turned off. 0x0114
06/03/2018 22:36:57 Device UPS: The graceful shutdown period has ended. 0x014F
06/03/2018 22:36:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
06/03/2018 22:36:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/03/2018 22:36:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
06/03/2018 22:36:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/03/2018 22:36:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
06/03/2018 22:36:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
--
There appears to be nothing in the UPS Fault logs.  The UPS Transition Logs do show distorted input earlier, but not during the recent shutdown.
1 06/03/2018 04:47:54.000 3 distorted input
2 06/03/2018 09:01:48.000 3 distorted input
3 06/03/2018 07:25:19.000 3 distorted input
4 06/03/2018 07:18:30.000 3 distorted input
5 06/03/2018 07:18:22.000 3 distorted input
6 06/03/2018 07:17:54.000 3 distorted input
7 06/03/2018 07:17:10.000 3 distorted input
8 06/03/2018 07:16:55.000 3 distorted input
9 06/03/2018 07:15:12.000 3 distorted input
10 06/03/2018 07:15:05.000 3 distorted input
Any ideas?  I'm worried it's just going to randomly shut all the outlets down again.
Matt
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

Thanks again Liam for your informative replies!

I've been an APC user for well over 20 years and I've been very happy with the products, so it's good to hear you think we have the right equipment for this site.

The Frequency being off in the data logs, is that something I should ask the local utility (DTE Energy) about? 

Could this be related to a problematic ground at all? We had some issues with Comcast last year and Comcast thought maybe our ground was suspect, but it appears solid to me (but I'm not an electrician).  I did have DTE check at the pole a year ago and they did replace some old taps, but otherwise said everything looked fine.

Matt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:25 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:25 AM

Hi Matt -

What exactly is connected to the UPS? Could you attach the data logs?

You may find that lowering the sensitivty setting of the UPS will reduce the instances of switching to battery due to input distortion.  this can be done via the LCD screen, Network Management Card, or Powerchute Business Edition.

Thanks

Liam

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:24 AM

Thanks for the reply Liam.  I have attached the data log.

Do you recommend LOW or REDUCED for Sensitivity? I'm currently on Normal. What are the dangers in doing this?

After I posted last night, I went ahead and did the firmware update to 9.9 and the Network Card up to 6.5.6 (it was on 9.1 and 6.5.0).

I have a variety of equipment attached including:

A Dell T320 Server, 2 Netgear GS724Tv4 switches, a Synology 916+ NAS, an old Netgear ReadyNAS PRO 6, a Ubiquiti EdgeRouter Lite, a Comcast cable modem/gateway and an Apple Airport Extreme.

I believe that is about everything attached.  I'll take another peek and make sure I didn't miss anything.

I did open a ticket with support.  They told me to power every down, unplug everything from the ups, disconnect the batteries, then reconnect everything and power it backup on.  They said this would reset the CPU in the UPS?

Matt

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:24 AM

Hi Matt - 

I would probably start with "Reduced" and keep an eye on it. If the unit keeps switching to battery, then go with "Low". The tradeoff is that your transfer time (the brief moment when there is no output voltage from the UPS) is extended. Most IT equipment has no problem with this, but occasionally you will find high powered servers that do not like the transfer time. In these (uncommon) situations where the load cannot handle the extended transfer time and the input power requires lower sensitivity the only real option is a Double Online Conversion UPS like our SRT models. This is not common however, and I would not anticipate that you will see any issues.

thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

Thanks Liam.

Out of curiosity, was there anything of interest in the UPS data log?  Anything that I should be worried about or have checked?

Also, do you think I should bother doing the "cpu reset", basically shut everything down, unplug all devices, disconnect the batteries, and reconnect and power up?  Is there value in doing that?

The problem has not happened again since I did the firmware updates.

I thought about a true-online UPS, but that is a lot more expensive of course.  I've always been a bit confused on this because some other competitors, like MinuteMan, offer "true" online UPS at a much lower price.  But I've always bought APC so I'm leery about going anywhere else.

I know I'm getting a little off topic here, but how does this relate to what I see marketed as a "true sine-wave" UPS?  I see that talked about a lot too.  

Realistically, should all the equipment I listed be able to handle the transfer time w/o issue?  Or is anything I listed more sensitive?

Thanks again.

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

Hi Matt - 

Everything looked fine in the data logs. Frequency seemed slightly off, but voltage was solid. This leads me to believe the issues you were seeing were related to THD or some instability in the utility power. If the issue has not returned, it's possible that it was just a temporary power disturbance and that there is no need to adjust the unit.  If you do adjust the unit, I don't think your load will have any issue with the transfer time. I don't think there is any need to perform the "brain dead" procedure that tech support recommended. 

The Online units do offer tighter power regulation and no transfer time. The power quality is definitely the best that can be had, and they are better at dealing with really poor quality input power. That being said, they are expensive and fairly complex. If there is not a pressing need for one, I really think that a standard Line Interactive Smart-UPS is probably the best bet for most applications in this size range. They're relatively inexpensive, reliable, and efficient. All Smart-UPS output a pure sine wave and are appropriate for IT environments. Given your application, I think your SMX1500 is probably the best tool for the job.

Hope this helps,

Liam

T

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

0 Likes
0
3601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:12 AM . Last Modified: ‎2024-03-07 03:24 AM

Thanks again Liam for your informative replies!

I've been an APC user for well over 20 years and I've been very happy with the products, so it's good to hear you think we have the right equipment for this site.

The Frequency being off in the data logs, is that something I should ask the local utility (DTE Energy) about? 

Could this be related to a problematic ground at all? We had some issues with Comcast last year and Comcast thought maybe our ground was suspect, but it appears solid to me (but I'm not an electrician).  I did have DTE check at the pole a year ago and they did replace some old taps, but otherwise said everything looked fine.

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore