Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Smart-UPS 1500 (SMT1500RM2U) output reverses polarity when on battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 (SMT1500RM2U) output reverses polarity when on battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5029
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ginbot86_apc
Lieutenant JG ginbot86_apc
Lieutenant JG

Posted: ‎2021-06-30 10:28 PM

0 Likes
4
1633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

Smart-UPS 1500 (SMT1500RM2U) output reverses polarity when on battery

This was originally posted on APC forums on 4/19/2016


I recently bought a Smart-UPS 1500 2U (SMT1500RM2U), and when I use a 3-prong receptacle tester, I noticed that the output's Hot and Neutral terminals reverse polarity when it switches to battery power. Once it goes back on-line, the polarity is correct again.

Is this typical of the Smart-UPS line-up? It seems like a bit of a design flaw for APC's newest UPSes to have this type of issue.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • hot-neutral
  • polarity
  • reverse
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:28 PM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

This reply was originally posted by Bill on APC forums on 4/26/2016


Hi,

When the Smart-UPS switch to battery it breaks Neutral (per UL requirements) and the Neutral floats. From H-N you will see 120v, but the split between H and N will fluctuate. I would be willing to bet that polarity tester is actually just looking for voltage on Neutral and that's why it trips. Kbase FA156549 "Why can I measure voltage between the ground and neutral wires when my UPS is on battery?" discusses the voltage when the Smart-UPS is on battery.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
vivekjm_apc
Ensign vivekjm_apc
Ensign

Posted: ‎2021-06-30 10:28 PM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

This was originally posted on APC forums on 4/20/2016


This issue is not unheard of. I can confirm one of my Smart UPS SUA2200I units reverses polarity at the outputs whilst running on battery. But I've not bothered to get it fixed. Maybe it's an internal wiring thing? Must check the other Smart UPS for this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

UnexpectedBill_apc
Captain UnexpectedBill_apc
Captain

Posted: ‎2021-06-30 10:28 PM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

This was originally posted on APC forums on 4/20/2016


The use of a "live neutral" configuration may be confusing your tester, although I'm not sure if the Smart-UPS is designed in that way or not. (I believe but have not proven that it is.)

Reply

Link copied. Please paste this link to share this article on your social media post.

ginbot86_apc
Lieutenant JG ginbot86_apc
Lieutenant JG

Posted: ‎2021-06-30 10:28 PM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

This was originally posted on APC forums on 4/20/2016


I tried with another non-APC power inverter that I know has a live/floating neutral, and that causes all 3 lights to glow on the tester.

I had a chance today to try the tester on some other rackmount Smart-UPS models. I forgot to write down the model numbers, but I found the 120V models to have either hot-neutral reverse polarity, or a floating ground with all 3 lights lit on the tester.

Strangely enough, the 208V models I tried have proper polarity when on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:28 PM

0 Likes
0
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM

This reply was originally posted by Bill on APC forums on 4/26/2016


Hi,

When the Smart-UPS switch to battery it breaks Neutral (per UL requirements) and the Neutral floats. From H-N you will see 120v, but the split between H and N will fluctuate. I would be willing to bet that polarity tester is actually just looking for voltage on Neutral and that's why it trips. Kbase FA156549 "Why can I measure voltage between the ground and neutral wires when my UPS is on battery?" discusses the voltage when the Smart-UPS is on battery.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.