APS Smart UPS 1500 - No LED or any lights after battery change...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APS Smart UPS 1500 - No LED or any lights after battery change...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
3
3869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

APS Smart UPS 1500 - No LED or any lights after battery change...

Changed the battery in APC UPS1500, put it back together, and no lights or anything. any clue what may have happened or how to fix it?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • APCLED
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:56 PM

0 Likes
0
3869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:56 PM

Rob,

Sorry for the delayed reply. Is the on line LED lit? That is the middle LED in the second row from the left. If it is then the UPS in on line and the batteries LEDs my light up once the battery pack charges.

You can check the battery pack charge with a DC volt meter. The unit has qty 2 12v batteries in series so the voltage reading would be around 27 volts DC for a good battery pack. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
0
3869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

Rob,

If the batteries are dead or not connected properly the unit will not power on and there will be no LEDs lit. Check the battery connections and if the Smart-UPS is SUA1500 check that the battery connector on the back is secure.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
0
3869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:57 PM

Thanks for the quick reply. I triple checked the battery connections, and checked the connector in the back, and all the connections looked good and tight. I do feel air from the fan vent in the side, and it beeps when you cycle the power button, just no lights whatsoever. It is still plugged in to the same place along with other devices that are all working so the AC power should be fine. When I shut it down to change the batteries, one of my servers was 'complaining' about lack of backup, but that went back to normal when the battery reconnected. Could the new batteries just be very low?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:56 PM

0 Likes
0
3870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:28 PM . Last Modified: ‎2024-03-06 10:56 PM

Rob,

Sorry for the delayed reply. Is the on line LED lit? That is the middle LED in the second row from the left. If it is then the UPS in on line and the batteries LEDs my light up once the battery pack charges.

You can check the battery pack charge with a DC volt meter. The unit has qty 2 12v batteries in series so the voltage reading would be around 27 volts DC for a good battery pack. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore