Posted: 2021-06-30 10:27 PM . Last Modified: 2024-03-06 10:57 PM
I have a APC 1500RMUNC, the outlet groups automatically turn off, an on. I have replaced the ups 3 times with brand new units. I have 150, of these ups in use at my company this is a new issue to me. Is there, a problem with the input power on the circuit that is causing this to happen ? I went through the logs, I don't see the unit switching to battery due to loss of input power. Thanks.
Posted: 2021-06-30 10:28 PM . Last Modified: 2024-03-06 10:57 PM
The issue has happened on multiple units at that location. There is not a power down schedule, or load shedding. I did check the unit for an overload condition, that doesn't appear to be the case. Since I changed the sensitivity, to low I"ve been having better luck. I will continue to monitor the unit. Thanks for you help.
What is the exact model number of the unit? You will find the information on a bar code stick on the back of the Smart-UPS.
When the power is cut to the outlet groups is anything logged? Also, is there anything attached to the unit via USB or Serial?
UPS Network Management Card 2
Hi, there is nothing attached to the USB or serial ports. There is nothing logged, no transfer to battery, or low volt. I did change the sensitivy to low.
If the issue is only happening with 1 unit it is possible the unit needs to be replaced. You should verify that there is not a power down scheduled on the NMC and that there is nothing configured for load shedding. Of course those events should be logged so I do not expect you will find a scheduled shutdown or load shedding. Some thing that could cause the issue is an over load. If the unit is over loaded it could shutdown abruptly.