Smart-UPS 2200 + NMC2 does 2 self tests.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 + NMC2 does 2 self tests.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
7
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

Smart-UPS 2200 + NMC2 does 2 self tests.

I am a little stumped on this one. The UPS keeps doing 2 self tests a day apart instead of one.

I have a NMC2 installed (9631) with the 6.40 software.

I set it for 7 or 14 days and when it is due for a test it will complete one, then do another the next day.

Since I spotted this I disabled self test on the card and checked the UPS config via the panel and it was also disabled. Set it for a 14 day test and left it alone thinking it was sorted.

Saturday and today it did a self test and I have no idea why it does the 2nd?

From the logs 

18.04.2016 10:30:14 Device UPS: RFC1628 MIB UPS test completed. 0x3603
18.04.2016 10:30:14 Device UPS: Self-Test passed. 0x0105
18.04.2016 10:30:06 Device UPS: Self-Test started by automatic timer. 0x0137
17.04.2016 08:36:51 System Web user 'apc' logged out from 192.168.1.10. 0x001F
17.04.2016 07:36:39 apc Web user 'apc' logged in from 192.168.1.10. 0x0015
16.04.2016 23:20:13 Device UPS: RFC1628 MIB UPS test completed. 0x3603
16.04.2016 23:20:13 Device UPS: Self-Test passed. 0x0105
16.04.2016 23:20:03 Device UPS: Self-Test started by automatic timer. 0x0137

Any ideas?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

That's what I recall with mine. If no tests are configured, you should still get one on a periodic basis to verify the battery is good to go when needed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

Hi,

What is the exact model and serial number of the Smart-UPS. You will find the information on the bar code sticker on the back the unit. 

If the model is SMT2200 or SMX2200 what firmware version is the UPS running? You will find the UPS firmware information and the model and serial number in the NMC under About - UPS or from the LCD panel under the About menu. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

Model
Smart-UPS 2200
SKU
SMT2200I
Serial Number
JS1112033918
Firmware Revision
UPS 07.1 (ID17)
Thanks.
On 4/18/2016 9:58 AM, Bill said:

Hi,

What is the exact model and serial number of the Smart-UPS. You will find the information on the bar code sticker on the back the unit. 

If the model is SMT2200 or SMX2200 what firmware version is the UPS running? You will find the UPS firmware information and the model and serial number in the NMC under About - UPS or from the LCD panel under the About menu. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

Hi,

The self-test parameters are stored on the UPS so the issue is with the SMT2200.

The firmware is up-to-date so you could reset the unit

1) Turn off and unplug UPS from wall
2) Disconnect Battery
3) You may hear an audible "click" from the UPS.
4) Reconnect battery, plug unit back in the wall, and turn UPS back on 

 If that does not resolve the issue and the unit is under warranty you could request a replacement.  

You could ignore the issue since it is cosmetic and running a self-test a day apart will not hurt the unit.

Another option is to set the UPS to not run an automatic self-test and run the test manually every 2 weeks.   

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

I have set it to "UPS Startup and every 7 Days since last test" and will see what happens in a week, if it does it again I will brain dead the unit and try it again.

Thanks Bill. 

Gareth.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:58 PM

I owned an SMT3000 that was on the 7.1 firmware that was doing the same thing.  This was the hardware revision level that could not be updated to the version 8.x firmware.  There is a known hardware issue with earlier revision units that will, indeed, execute a self-test even when one is not configured or, in your case, two if you configure one test.

Being OCD, I replaced my unit, but if I were to do it all over again, I wouldn't care.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

Thanks Joe, I have now set it to do one at startup  as it still  did 2. I assume it will throw in a regular  extra one for the fun of it. I can live with this if it does as I expect.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

0 Likes
0
1725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:27 PM . Last Modified: ‎2024-03-06 10:57 PM

That's what I recall with mine. If no tests are configured, you should still get one on a periodic basis to verify the battery is good to go when needed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.